Hello

Couldn’t find anything in the forums on this and thought I would have…

Large warehouse, minimal power circuits, two or three lighting circuits, max of 5 three phase circuits.

Would it be acceptable to run these within the metal purlins at roof level and tied in place or would tray hung from purlin clips be required?

Trying to avoid this if possible as some of the tray may be ran 30m for the sake of one cable for example

Thanks
 
Are they z purlins? Ie theres already a trough formed for you to lay them in? NYYJ layed in there would be fine by me, they aint ginna fall up! But if its farm or risk of vermin I'd use swa. Use beam clips to support things if you need to traverse any other steels or vertical drops

To add just be aware of grouping
 
Last edited by a moderator:
I see and have put cables in purlins as you describe, but its never the first choice. If the cables are inside the purlin you are only one screw away from cable damage if a roofer or cladder come along. You would be surprised how long the screws used by roofers can be. "Why use a 2 inch screw when i have a couple of hundred 4 inch screws", lol -
If i was planning from scratch i would use my own containment, see it as an investment for the future
 
I see and have put cables in purlins as you describe, but its never the first choice. If the cables are inside the purlin you are only one screw away from cable damage if a roofer or cladder come along. You would be surprised how long the screws used by roofers can be. "Why use a 2 inch screw when i have a couple of hundred 4 inch screws", lol -
If i was planning from scratch i would use my own containment, see it as an investment for the future
Ive only ever done it after a roof is on, and no ceiling is being fitted, ie its all left exposed
 
Ive only ever done it after a roof is on, and no ceiling is being fitted, ie its all left exposed
I am referring to subsequent cladding and roofing upgrades to insulated roofs, i have had it on two buildings where repairs / upgrades have damaged cables (not ones i have installed, i might add... :cool:
 

Reply to Running Cables in Purlins in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
933

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
490

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top