I’m getting conflicting information from electricians at my works regarding the correct way to terminate SWA and more notably S/Y cable.

I was shown a few months ago that with s/y you only Earth the supply side of the shielding (like you would win data)

I was also under the impression you do the same with SWA.

Both are the case if you have a dedicated conductor for cpc. I thought this was the case so that there is no parallel cpc path.

Can anyone clear this up?

Thanks
 
Both ends should be terminated using the correct glands however it is only necessary to earth one end, preferably the supply end.
 
If I was glanding an swa from a plastic enclosure to another plastic enclosure then I would earth the supply end as it were with a banjo with a fly lead, if a separate cpc is being provided by another core
The other end I would gland but not provide the fly earth.
Or from a metal enclosure at the supply to say a plastic enclosure I’d do the same thing.
As long as the armour is connected to earth where ads is the choice for fault protection as it is considered an exposed conductive part.
I don’t like to use s/y and earthing the braid is for screening as the braid is not acceptable to be used as a cpc in its own right
 
Last edited:
Thankyou Ian. That it how I see it.

Iv been told by a year 3 apprentice that they teach you to Earth both ends of the s/y as standard.

I can’t see how that is the right way
 
There's nothing wrong with earthing both ends as long as the braid is not used as the CPC
 
HOw do you Earth both ends without it being part of the cpc?

So for example on the supply side the braids are connected with the cpc. If you do the same on the other side then it’s actually part of the cpc??
 
HOw do you Earth both ends without it being part of the cpc?

So for example on the supply side the braids are connected with the cpc. If you do the same on the other side then it’s actually part of the cpc??

It's just ends up a parallel path. Not the cpc, it will need disconnecting at one end temporarily to test R2 the same way SWA should be.
 

Reply to S/Y and SWA termination - stupid 25 characters in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
502
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top