Well I had a very interesting telephone conversation from a tech guy at Kraus Naimer about removing links in the DC isolator and as you might well of guessed it isn't black and white! I hope he will stand by his word and email me what we discussed so I can post on here but until then I hope this may help (a little) but please this is not 100% and don't take my word for it.

Their range of DC isolators is divided into 4, 6 and 8 pole devices. 4 pole rated to 200V, 6 pole to 600V and 8 pole to 800V. He recommends never removing links from the 4 or 6 pole isolators (T104, T106) but when it comes to the 8 pole (T108) he said it may be possible to remove only two links (one each pole) to render them 4 pole BUT it reduces the voltage to 400V. So if the array string is less than 400V it is possible to use one DC isolator for two strings. It also reduces the contact amperage considerably. He did say that considering the cost of a DC isolator he found it puzzling why someone would prefer to do this?

Like I say please don't consider this as a statement of fact merely as passing on a telephone conversation. Your job your risk!
 
Interesting stuff. Makes sense.

He did say that considering the cost of a DC isolator he found it puzzling why someone would prefer to do this?

Errr, because his rep was telling people they could perhaps?! :-)
 
Had a email form K&N today. See below and PDF's:

Hello Mark,

Please find attached data sheets which show the amended connections required to use our T104, T106 & T108 disconnect switches for isolation of two PV strings. Rating data for the two string operation is also included.

The following points should be noted with regard to implementing these changes.

  1. As there will be twice the number of cables to be accommodated in the enclosure, it is important to ensure that the enclosure has sufficient cable entry holes and that the cables being used can be accommodated in the enclosure.
  2. Cable entry is often necessary via both the top and bottom entries in the enclosure.
  3. The rating date provided is based on selecting by DC-21B utilization category in order to maximize the current rating at each listed voltage. The potential disadvantage is a reduced number of switching operations, but in view of the application, this is most unlikely to represent any problem and most of our competitors use DC-21A or B as the selection criteria for their PV switch-disconnectors.
I am happy for you to circulate this information to the members of your forum provided the comments above are also included.

Please call if you would like to discuss any points.

Kind regards,
Denis

Denis Thomas
Technical Sales Manager
 

Attachments

!!!!!!!!IGNORE ATTACHMENTS ABOVE!!!!!!

REASON......


Hello Mark,



I have found a typing error on the data sheets – in the text above the single string diagram. Corrected documents attached.



Kind regards,

Denis
 

Attachments