Scenario where lack of supplementary bonding is dangerous | Page 2 | on ElectriciansForums

Discuss Scenario where lack of supplementary bonding is dangerous in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 2, 2023
Messages
14
Reaction score
2
Location
Coventry
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a dwelling provided a) the main bonding is in place and b) the CPC’s of all circuits are connected together in the CU (as they will be).

Consensus is on an EICR code 2 where there is no RCD for additional protection and supplementary bonding is not in place. What is the potential danger ? What am I missing ?
 
@Falkus and others, out of interest how would you code this one that I’m about to do:

The bathroom light needs changing anyway as it isn’t IP rated.
Must be a very low ceiling to code it for not being ip rated :)
 
Must be a very low ceiling to code it for not being ip rated :)
It is, and I'm not exactly short of reasons to condemn this light!

[ElectriciansForums.net] Scenario where lack of supplementary bonding is dangerous
 
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and radiator pipes could well have a voltage introduced onto them via things like the boiler electrics or immersion heater, the cold could well be isolated from all other pipework yet be at earth potential due to the cold supply pipe coming out of the ground, you could well have 230V across the two taps.

The hot/cold/radiator pipes were the only things that needed to be bonded when I started out and of course there wasn't any RCD on immersion and lights back then, only sockets, so it made sense. It was only later that we had to bond the lights/towel rad/shower etc along with the pipework, this made less sense to me than doing the pipework as everything was effectively bonded together at the consumer unit anyway. I get that a 4mm earth will have lower resistance than the cpc but you were allowed to use the cpc of the thing in the bathroom you were bonding anyway, you could bond the electric towel rad at the spur outside, not directly to the rad and the 1mm cpc acted as the bond, bizarre really some of the regs they come up with.
 

Reply to Scenario where lack of supplementary bonding is dangerous in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I hate to tell you this but if you don’t have a paper trail or a contract with the original price to wire your home, the electrician can put a...
Replies
9
Views
1K
  • Question
No sane person 'trusts' a Voltstick for anything, other than if it lights up when a circuit should be dead, it means that something is not as...
    • Informative
    • Like
Replies
24
Views
7K
  • Question
I know you’ve all be waiting in suspense for the next exciting update in this story. I promise this one will be much shorter! The OH was back at...
Replies
21
Views
4K
Yes of course I was lucky enough to do heating controls nationwide and majority required bonding to tank most were a pain in the arse ?‍♂️ I was...
Replies
12
Views
8K
  • Question
Indeed, even if you carefully followed every detail in guidance note 3 the defect would go unnoticed.
2
Replies
29
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks