What I am saying is ' protection by barriers and enclosures' can only be done by inspection, not testing
 
I will have to put my hands up and say that I am wrong. Just had a look at 612.4.5, and they tell you about it...

So as Stumas says, if you have a collection of test fingers, you can do it.

[ElectriciansForums.net] Schedule of items inspected


Never thought that it would be as easy as that though, so if you can test to IP2X or IPXXB, or IP4X or IPXXD then you can tick the box! :)

Always happy to be corrected, but I think it would be a LIM in there for me, not an N/A anymore. This is why I love to discuss!
 
Last edited:
Live parts must be protected against direct contact by insulation. If the insulation is applied during the erection of the installation, the quality of the insulation must be verified by tests equivilant to those required in British Standards for similar equipment. It is generally completly impractible for installers to apply such tests on site and therefore the use of factory build assemblies is preffered.
So if you have not built the assembly and provided the insulation yourself then it is N/A in relevant box.
 
Last edited:
Live parts must be protected against direct contact by insulation. If the insulation is applied during th erection of the installation, the quality of the insulation must be verified by tests equivilant to those required in British Standards for similar equipment. It is generally completly impractible for installers to apply such tests on site and therefore the use of factory build assemblies is preffered.
So if you have not built the assembly and provided the insulation yourself then it is N/A in relevant box.

Are we thinking about site applied insulation now, as that seems to be more what that is...

I think this may be where I have had a bit of a cross over, as they were both together on the old 16th sheets. I can't even think at the moment whether site applied insulation is still a tick box on the 17th sheets, is it?
 
Are we thinking about site applied insulation now, as that seems to be more what that is...

I think this may be where I have had a bit of a cross over, as they were both together on the old 16th sheets. I can't even think at the moment whether site applied insulation is still a tick box on the 17th sheets, is it?




site applied does not seem to appear on 17th but inulation of live parts does im getting a headache see you soon and thanks lol
 
Never,you cannot put n/a in that section, to me, barriers and enclosures means,damage to the cover of a db, socket outlet, light switch, ad box, etc which could result in access to live parts is v necessary to the inspection
 

Reply to Schedule of items inspected in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
525
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
1K
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
273

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top