So its a less accurate Zs of the circuit, because it is being measured whilst the main earth is connected, & hence, as you say, parallel earth paths are introduced into the equation.
The true Zs of the circuit would therefore be if two tests were made. The first, for the Ze, (at the origin of the installation, & thereby avoiding parallel earth paths) & the second, the R1+R2 at the specific circuit, & then combining the two.
Although, as you say, the two could be combined into one test, but this then is less accurate then the above, due to parallel earth paths.