Screening control cables | Page 4 | on ElectriciansForums
Discuss Screening control cables in the Commercial Electrical Advice area at ElectriciansForums.net
Only symmetrical conductor arrangement inside the cable should be used with the variable frequency drives, to avoid formation of standing waves and increased voltages. The same thing as with coaxial RF feeders (SWR meter, if reflected wave is higher than 1:1 then it gets inside the RF amplifier output stage which destroys the transistor or losses power and efficiency).
SWA steel armour is incapable of proper shielding against those awful harmonic frequencies asociated with VFD (kinda same effect like with sine wave clipping), so there is a reason why only silver coated copper shielding is used on proper radio frequency coaxial cables, or they use just thin flexible tubes with fine foam as an insulation.
Even when the same symmetrically arranged cable or coaxial cable is squeezed at one point then good standing wave ratio can be ruined.
Had a good look at the CY screen today and it is copper, from the look of it and the way I blunted my snips I thought it was fine steel wire!
Think I'm going to return those side cutters!!!
pound land special?
bahco hdg or knipex snips (160/180mm)
behco hdg snips are rated to cut piano wire and they can cut small chain down easily as well
These are Bahco I don't buy cheap rubbish from eBay or anywhere else, I expect tools to last and don't mind if the price matches!
I've not had them long and only cut control cables and flexes with them I use a different pair of croppers for steel braid
So they're going back I'll try another pair just in case they're a dodgy batch, quite disappointed really as I do like this brand!
Although their customer service isn't great......
Recently I enquired direct about a replacement box for the 1/4" socket set I've had for 4/5 years the hinge wore out, so I contacted them re buying another to replace it,the guy said they didn't sell them and he'd see if he could sort one out for me ,I've emailed him several times with no response at all, which is pretty poor I think !
which bahco snips?
[ElectriciansForums.net] Screening control  cables
i use these and they are very good 20hdg
In general ferrous metals like steel are prone to formation of eddy currents which generate heat especially at the VFD harmonic frequency range, roughly from 4kHz to 30kHz.
Actually, as far as I ''know'' it's more of an issue with single core cable and steel armour, with multi-core cables it's not so significant cause electromagnetic waves induced in steel armour from two conductors cancel each-other out.
How do you normally terminate the pigtail of sy cable steel armour to commando plug at the supply end only to protect against cable mechanical damage?
I couldn't find anything about connecting two dissimilar metal wires (green-yellow earth conductor with galvanized steel armour). I think crimping them in to one ferrule is not the best thing do.
The pigtail should be as short as possible to reduce inductance, only thing is it depends on frequency range you want to screen against with considering that steel works better at low frequencies. SWA cable steel armour is connected at both glands cause there is a 360 degree connection. If you don't have a EMC grade glands for sy cable then there is no other choice but to use pigtails and connect with short one only at the supply end to avoid ground loops.
Reply to Screening control cables in the Commercial Electrical Advice area at ElectriciansForums.net
Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...