Probably made in china........

I think one of these is called for here :D

[ElectriciansForums.net] Secondary Switchboard for kitchen from Primary Switchboard
 
Radials are safe and have thier place in the uk.
rings are also safe and also have thier place in the uk.

the idea of running a sub main to a second CU in domestic setting is admirable but over complicating a simple job, you should not use circuit breakers as switching for your appliances, firstly they are not intended to be used for regular on off actions, this could cause wear and ultimately failure.

the 10mm cable can carry 64a, BUT that's makes 2 assumptions,
first
its flat twin and earth
second
its clipped directly to the wall, without being enclosed or covered with insulation.

so with those 2 assumptions satisfied yeah you could potentially upgrade to a 63a mcb/Rcd combination, but they are not likely to be satisfied, as you don't want anything on show, so worst case scenario is the cable can only carry 32a.

when you had an electrician on site and he advised you, he is the best person to listen to, for all the advice we have given has been given on the information YOU have supplied, but with your limited( and that's being kind) knowledge of bs 7671, you may have left out some very valuable information, like the construction of the building, or that your 17th century mansion has its own power station which runs on 110v.

get an electrician in, tell him what you want including some central controls, then let HIM tell YOU the best way of doing it, not the other way round. Laws and regulations need to be satisfied before any consideration of your aesthetic opinion.
 
but don't get the spark who advised that you need a separate MCB for each socket outlet. he's got less knowledge of electrics than i have of piloting a helicopter.
 
the idea of running a sub main to a second CU in domestic setting is admirable but over complicating a simple job, you should not use circuit breakers as switching for your appliances, firstly they are not intended to be used for regular on off actions, this could cause wear and ultimately failure.

There's nothing admirable about running a sub-main to a separate CU, for a typical run of the mill domestic kitchen!! If the house was the size of a mansion, that would may be another matter!!

This guy is a total idiot, and isn't going to listen to anyone. Best leave him to his own devices!!
 

Reply to Secondary Switchboard for kitchen from Primary Switchboard in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
817
  • Question
Thats why somebody told you to spk to the sparky
2
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top