Evening Guys

Need some "light" shedding if possible on a PME Installtion

About to change a secuirty light which is wired to the light circuit.

Live to Neutral 0V
Live to Earth 230V
Neutral to Earth 230V worrying

The cabling is almost impossible to trace it goes into the wall down and "disappears." I have lifted the boards I can get to but now need to start knocking the wall down to physically trace the cable.

Turning off the light circuit downstairs I get 0V so its definately connected to that circuit . Killing the sockets has no effect

I get continuity for earth and line to the nearest light fitting but not for neutral.

New consumer Unit Installed about 6 months ago , but not sure if the light was working before that. Any suggestions welcome.

Just to confirm the light is wired to a 3 way light switch for the hall and landing but only the line is connected, there seems not to be a return to the light yet it still functions by switching the switch so totally at a lost.

All voltage light fittings downstairs are correct.

Still a newbie so be gentle :)

Any advice appreciated.
Many thanks


Thinking about just cutting and replacing but would rather solve the issue.
 
Last edited by a moderator:
thanks MFCtitch - having to retrain to a totally new career is hard and I take the critism in the hope of clarification !!
We may be new but we are only trying to be safe and reaasure ourselves
cheers and good luck
 

Reply to Security Light Nightmare in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
681
Also posted in DIY. strange one in my kitchen. 3 sets of 2-way switched mains GU10 Philips down lighters. ( no dimmers) Have been fine for...
Replies
0
Views
150

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top