hi

when running a 10mm bonding( seperate to the cpc proctected distribution circuit) conductor for a pme supply to a detached garage that contains (water/gas services) is it ok to run from exisitng house cu to gargae cu and then bond the services to garage cu. or does the bonding conductor have to be unbroken all the way back to the house cu

many thnaks
 
if you are using the house earthing for the garage then the extraneous metalwork in the garage needs to be bonded to the house MET ( min 10mm )
 
hi

when running a 10mm bonding( seperate to the cpc proctected distribution circuit) conductor for a pme supply to a detached garage that contains (water/gas services) is it ok to run from exisitng house cu to gargae cu and then bond the services to garage cu. or does the bonding conductor have to be unbroken all the way back to the house cu

many thnaks
Yes it is.
The two earth bars in the CUs become Earth Marshalling Terminals.
No the conductor doesn't have to be unbroken back to the house CU, or to the MET.
 
so if you export the pme to the garage CU via the seperate 10mm bonding conductor would you only earth the supply cable at the house cu and not terminate at the garage cu ???? or just connect the supply earth as well
 
Last edited:
i take it your running armoured to the garage..?..yes?....if so then earth the armourings at the house end only......then use the CPC of the armoured together with the seperate 10mm earth cable together...parrallel em up..both ends...into the garage C/Us MET....then take the 10mm earthing cable you exported from there to extranious conductive parts within the garage..(water and gas)......keep it continuous...that is to say you go to the first extranious point...lets say gas....bare the cables insulation off....enough to terminate into a BS951 clamp..BUT DONT CUT IT...KEEP IT CONTINUOUS...then from there to the water...or vice versa...from water to gas...depends which service is nearer to the garage C/U of course...
 
One of the problems with using both the armour and the bonding conductor jointly, is that you would have to guarantee that the armour is of a sufficient CSA to withstand the unknown current that may flow in it.
You would also have to guarantee that the circuit conductors would not suffer from the increased temperature caused by the unknown current flowing in the armour.
 
wouldnt use the armour for the cpc or main bonding conductor. would use either seperate 10mm main bonding conductor or use the cpc (3rd core of the swa if 10mm or above) The armour wouldnt have the required csa nessacary
 
You cant export the earth on pme if there is water or gas services in the outbuilding unless you have permission from the energy supplier.
You would install a rod then bond from outbuilding consumer unit
Terminate exported cpc at garage end in plastic enclosure so that the two earthing systems are totally seperate
 

Reply to seperate bonding conductor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
A lot of external bonding or earth conductors are bare copper strips. If mechanical damage is likely, then run some steel conduit… but all UV...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top