I was at a job today replacing a db and wiring supplies for an ASHP. The house used to be owned by a company who let them out (there's another 6 houses) as holiday cottages. The supplies were from a central board in cupboard on the site. The houses have been sold off and part of the deal was that they would pay for individual dno supplies and meters in outside boxes at each house . A firm was employed to run supplies from these meter boxes to the existing db's in the house. They have run a 3 core Swa terminated in a tp 63amp mcb using brown for live, black for off peak live, grey for neutral and the armour as the cpc. To me this isn't correct but I'm looking for of you guys expertise. Inside the house it was terminated into a 4 pole isolator and split into seperate db's. I was removing the need for the off peak supply so I fitted a switch fuse and used the Swa using a core as L,N&cpc but the other properties are as described above.
 
What if, for arguments sake the domestic is pulling 50amps and the off peak pulling 50amps.

They can't, as the total of the two is flowing through a 63A OCPD.
 
Here goes, don't often get to calc something up out here...
16mm Copper = 1.15 Ohms/km
3c PVC SWA = 3.2 Ohms/km (Armour CSA = 50mm) (I'm Assuming 70degree)
1.15 / 3.2 = 0.3594
16 x .3594 = 5.75
50 / 5.75 = 8.7mm (CPC = 8.7mm)

16mm passes as an EARTH WIRE (Table 54.7 BGB)
FAILS as a Bonding conductor (GN 8 - Table 5.1 and Table 54.8 BGB)

Like I said its been a while, out here put in the biggest CPC/EC you can get as the high Z reading internal at the Genny's is enough to fail ring circuits only 50 feet away (unless you use Type 'B' 3A MCB's all over!!!!)

Now to wait for incomming from E54 !! :89:
 
I don't know what you are expecting, i'm not even going to check your calculation, because i already know the armouring of a 3 core 16mm SWA cable will not comply as a bonding conductor, only as a CPC!!

As for your Ze, or should i say Ra, it wouldn't be a bad idea to get that high value down to sub 1 ohm. So what are the relevant internal impedances of these gen sets your using over there, because something just doesn't sound right to me?? lol!!
 
Ra are anywhere around 0.5 - 150 Ohms depending on the site and the amount of copper banged in the earth! (reading gained from disconnected EC at the MET using Method 1)

The internal Zgen (impedance) of the generators before the distribution system (T/S - MDP - SDP & then CDP + circuit resistance) can be enough of a high Zs to fail a Type B 32A MCB, this morning one refurbed genny (FG Wilson) had a Z of 0.5 Ohms at the incomming side of MCCB (genny running, MCCB switched off incomming earths disconnected) then you add the resistance of the distribution network, joints/connections through the system etc. It all pushes the Z up.

But enough of my gripe it makes life a challenge.
 
If the on peak and off peak supplies originate from the same single dno fuse then it cant really be considered a "shared neutral".
What should be of more important design consideration is achieving proper discrimination between all the various protection devices in series from origin to final circuit.
 
Please correct me if I'm interpreting this wrong but does a 16mm SWA (70 deg) not comply for main bonding purposes as it provides a copper equivalent of 22.1mm?
For the use as a protective conductor you use the formula using the respective k values for the appropriate materials.
In this case 143 for the copper line conductor and 46 for the steel armour.
Then the steel csa for 16mm² 3 core SWA is 50 mm² so the copper equivalent = 46/143 *50 = 16.1 mm² this is suitable as a circuit protective conductor.

For use as a bonding conductor you compare the resistivity values for copper and steel which have a ratio of 1:8.5 (1.7*10-8Ωm vs ~14.3 *10-8Ωm)
Then the steel csa for 16mm² 3 core SWA is 50 mm² so the copper equivalent = 50/8.5 = 5.88 mm²
which is not suitable for the 16mm² minimum size for a bonding conductor (from table 54.7)
 

Reply to Shared neutral in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
851

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top