I’m planning on putting in a small (10x10) detached shed for garden storage plus a freezer for meat storage, an in-wall AC unit (for temperature sensitive seedlings), and a few outlets and lights. The interior would be fully insulated and Sheetrock finished. I was planning on a 100amp,12 position, sub panel with a buried conduit service from the house (about 30’). There would likely be a minimum of four circuits, two appliance (fridge and AC), one for outlets and one for lights (both GFI’ed). The question, do I need an external device disconnect, for firemen access, or will a main breaker in the sub panel be OK? The shed could be locked a lot of the time, so interior access might not be always possible. Also, will the shed need it’s own grounding rods?
 
I’m planning on putting in a small (10x10) detached shed for garden storage plus a freezer for meat storage, an in-wall AC unit (for temperature sensitive seedlings), and a few outlets and lights. The interior would be fully insulated and Sheetrock finished. I was planning on a 100amp,12 position, sub panel with a buried conduit service from the house (about 30’). There would likely be a minimum of four circuits, two appliance (fridge and AC), one for outlets and one for lights (both GFI’ed). The question, do I need an external device disconnect, for firemen access, or will a main breaker in the sub panel be OK? The shed could be locked a lot of the time, so interior access might not be always possible. Also, will the shed need it’s own grounding rods?
You are on the right track and 100 amps sounds a little big for a 10 by 10 building but yes you can install a sub panel and what I do is a main lug only panel. You need to pull 4 wires with being 2 lives, 1 neutral and 1 ground wire, and your building does not require ground rods. Install a breaker to feed the building in your main panel and you are not required to have a disconnect on your building like you do your house. Your ditch needs to be at a minimum of 18 inches deep. Try a 60 amp panel and you should be fine.
 
I had to look up 'nail plates' over the pond as they are not really seen in the UK. For those how have not seen examples, here are the things:

The UK rules here are a bit different, we need RCD protection (GFCI at the panel) for buried cables less then 50mm (2") from wall surfaces and that lack earthed armour or similar means to automatically disconnect on penetration damage. We also define "safe zones" where cable ought to run so folks know not to hammer in stuff and that also has distances from wall surfaces, etc:

Of course folks still drill in to the zones they should not, and folks still run cables outside of where they should. Such is life!
 

Reply to Shed electrical requirements in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
603
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top