J

Just

Hi I have a socket Radial off a 20A MCB and a lighting Radial off 6A MCB in a shed the board is fed by a 32amp MCB protected by an RCD on a TNCS syatem in the house. If I want the first point of fault ie the shed to trip first should I be using an RCBO for a TT system that trips under .2s? This would avoid both RCDs or the one in the house tripping first if I use an RCD 0.4s disconnection. I could change the type of RCD in the house but that protects a number of circuits. I have a 4 way CU so could either have a RCBO main switch, protect two MCBs with a different type RCD or fit two RCBOs. Too many options!
Thanks for your advice,
 
What exactly is your problem ezzzekiel?
I have not argued (rationally or irrationally) against your suggestions, just pointed out that it will be messy or costly.
However I would point out that you have ommited any form of overload or fault current protection for the cable supplying the shed.
Are you suggesting that the main fuse be relied on to provide this?
 
Last edited by a moderator:
However I would point out that you have ommited any form of overload or fault current protection for the cable supplying the shed.
Are you suggesting that the main fuse be relied on to provide this?

you are correct but in my opinion no protection for overload or short circuit is required as this would only result in a more costly install
 
you are correct but in my opinion no protection for overload or short circuit is required as this would only result in a more costly install

Maybe I misunderstood you Ezzzekiel but if your splitting tails to a suitably rated enclosure would this than not house a suitable protective device for the SWA? Or am I reading it wrong?
 
hello everyone.

if the supply to the shed is a suitably rated CB protected by an RCD then whats wrong with this.....? if you dont wanna spend money? lot of hassle splitting tails, 2 RCDs is unnecessary complicaton... upstream will trip first (0.00000003s ha ha) then the other due to a shorter fault path... well yeah both basically.... The problem is the lazy bugger that cant be bothered to walk back into the house when the RCD trips...! haha just kidding mate... if the install is sound then the RCD shouldnt trip......
 
Maybe I misunderstood you Ezzzekiel but if your splitting tails to a suitably rated enclosure would this than not house a suitable protective device for the SWA? Or am I reading it wrong?

yes simon you are correct the enclosure would house a suitably rated circuit breaker to provide overload and short circuit protection with swa then running to shed (mech protected so no rcd required) terminating into a two way rcd protected consumer unit which would enclose circuit breakers rated for the circuits they protect.

Also a neat install can be made at little or no major additional costs.

also a big argument on exporting earths on tncs systems but thats another day :)
 
Last edited by a moderator:
The first thing that should be established is whether the Zs at the shed CU are low enough to allow the use of an MCB for earth fault protection.
If Zs are acceptable then we have two options.
We can go with ezzzekiel's first suggestion which would entail changing the Main switch at the house CU back to a non-RCD switch and install RCBOs for whichever house circuits require RCD protection. Install an RCBO at the shed CU for the socket-outlets. This will probablly entail using 8 or 9 RCBOs.
Or we could go with ezzzekiel's second suggestion involving splitting the tails, installing an enclosure, should be able to re-use the MCB from the CU and install an RCBO at the shed for the socket-outlets.
To my mind the first option would be the neatest, but costs could be prohibitive.
The second option would be messy, and from a legal view point may entail contacting the electricity supplier for a disconnection to install the Henly blocks.
 

Reply to Shed Installation Disconnection time? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
135
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
915
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
994
  • Question
Hi All, Looking for some advice into my build. What I've basically done is add additional RCD protection to my 100% off-grid 12V 3300W Inverter...
Replies
0
Views
186

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top