Hi I have a socket Radial off a 20A MCB and a lighting Radial off 6A MCB in a shed the board is fed by a 32amp MCB protected by an RCD on a TNCS syatem in the house. If I want the first point of fault ie the shed to trip first should I be using an RCBO for a TT system that trips under .2s? This would avoid both RCDs or the one in the house tripping first if I use an RCD 0.4s disconnection. I could change the type of RCD in the house but that protects a number of circuits. I have a 4 way CU so could either have a RCBO main switch, protect two MCBs with a different type RCD or fit two RCBOs. Too many options!
Thanks for your advice,
 
There is already confusion.
If we were to alter an existing non-RCD protected RFC, by simply changing an existing single socket to a double, would there be any requirement to provide RCD protection, and where would that protection be required to be placed?
As it stands if the socket is intended to be used for a specific item or items of equipment then there is no requirement for RCD protection. However if the socket was intended for general use there would be a requirement for RCD protection. This could be achieved by either the use of an RCD socket or by placing the RCD at the origin of the circuit.
If however you believe that the circuit requires protection, then the RCD would have to be at the origin of the circuit.
Simple enough if the CU can accept an RCBO, not so simple if the CU can't.
Before you know it, you are looking at a board change and all the attendant inspecting and testing; completely unesseccary as at most all that is required is the installation of an RCD socket.

You digress.

Aah well, you can lead a horse to water... as the saying goes. I'm afraid i won't reply to this thread again. As i think Ezzzekiel said earlier "you can be the boss". Well done :rolleyes:
 
I don't believe that I have digressed.
I have attempted to show that an erroneous belief that all circuits are required to have RCD protection can lead to costly uneccessary work.
A great deal of Local Athority housing uses earthed conduit, and often alterations and additions have used surface trunking.
There are also many converted properties where internal insulation has been applied to external walls enatailing that existing wiring is now at a depth greater than 50mm.
There are many instances where uneccessary RCD protection has been provided, often resulting in non-compliance with other Regulations.
To my mind, if we start with the premise that not all circuits require RCD protection, we will have a better understanding of when and where protection is actually required.
However as you say, you can lead a horse to water...
 
A circuit is an assembly of equipment supplied from and protected from overcurrent by one protective device. This would include cables and sockets. Ordinary twin and earth (which must make up 95%+ of domestic cabling) that is either not surface mounted or deeper than 50mm or mechanically protected/protected by earthed metallic covering
will require rcd protection regardless of location. Reg 411.3.3 specifically talks about rcds for additional protection.

I couldnt agree more.

411.3.3 this is one of the most well known new regs to conform with BS7671:2008

Sockets generally need RCD protection and in this case definitely. Unless you want to wire the shed in metal conduit!!!
 
Last edited:
Hello everyone!! :)

I'm a (very) new member here, and would first of all like to tell you how much I am enjoying this excellent forum - particularly this thread because at some time soon I have to wire-up two garages - both at the bottom of gardens and one of them is to a house with a TT system, so thanks to all of you for your very usefull comments.
 
arghhhhhhhhhhhhhh somebody shoot me please!!!

I do agree..! im just debating a few points.....


icon1.png
Shed Installation Disconnection time?

Hi I have a socket Radial off a 20A MCB and a lighting Radial off 6A MCB in a shed the board is fed by a 32amp MCB protected by an RCD on a TNCS syatem in the house. If I want the first point of fault ie the shed to trip first should I be using an RCBO for a TT system that trips under .2s? This would avoid both RCDs or the one in the house tripping first if I use an RCD 0.4s disconnection. I could change the type of RCD in the house but that protects a number of circuits. I have a 4 way CU so could either have a RCBO main switch, protect two MCBs with a different type RCD or fit two RCBOs. Too many options!
Thanks for your advice,

Where does the current install not comply? its rcd protected etc.... understand you may need to TT the shed and keep it seperate depending on whats its made of etc.... I dont see why you need to do anything.... can some enlighten me on what im missing?
 

Reply to Shed Installation Disconnection time? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
135
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
915
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
994
  • Question
Hi All, Looking for some advice into my build. What I've basically done is add additional RCD protection to my 100% off-grid 12V 3300W Inverter...
Replies
0
Views
186

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top