Hi guys am new to this forum

Can someone give me advice on shed power

I am looking at running power supply to a shed which will have a small chest freezer and few sockets for dewalt battery charger I was going to run 2.5mm swa cable straight form house cu (which is rcd protected)
The shed is approximately 40m away
 
There are a lot of other factors to take into consideration. What is the installation method for the cable? How much current have you calculated you will need? Is the shed metal or wood and which earthing method is used? And you don't need to have rcd protection on an swa cable with earthed armour but you may require rcd protection on any circuits fed from it.
 
Welcome to the forum mate.
Also to add to the above, you have to take voltage drop into account. 40 meters is a long distance.
2.5mm SWA cable over 40 meters will give you about 10A before you go over the 3% drop. (Im presuming you will want a light in your shed)
 
There are a lot of other factors to take into consideration. What is the installation method for the cable? How much current have you calculated you will need? Is the shed metal or wood and which earthing method is used? And you don't need to have rcd protection on an swa cable with earthed armour but you may require rcd protection on any circuits fed from it.
Method of installation is clipped direct
Current is need small chest freezer and battery charger for dewalt cordless power drill for example
Earthing it will be going back to main CU

My plan is to not have garage board in shed just straight sockets as it is pulled very little current

Both charger and freezer are on a 13amp plug socket
 
Welcome to the forum mate.
Also to add to the above, you have to take voltage drop into account. 40 meters is a long distance.
2.5mm SWA cable over 40 meters will give you about 10A before you go over the 3% drop. (Im presuming you will want a light in your shed)
Yes bud that is correct 1 small led light outside door and batten style led in shed its self
 
Yes bud that is correct 1 small led light outside door and batten style led in shed its self

As it stands at the moment you are looking at a supply of just under 10A for a 2.5mm SWA cable at 40 meters.
That's not enough for your stuff.
Also this work falls under Part P and is notifiable.
Might be good to get an electrician in to do it. Or for you to help out and save some money.
There is a great guy who lives your way. @telectrix . I got him round when I had issues with a lighting circuit.
 
As it stands at the moment you are looking at a supply of just under 10A for a 2.5mm SWA cable at 40 meters.
That's not enough for your stuff.
Also this work falls under Part P and is notifiable.
Might be good to get an electrician in to do it. Or for you to help out and save some money.
There is a great guy who lives your way. @telectrix . I got him round when I had issues with a lighting circuit.
I am a trainee electrician but am struggling to find the right information for this subject
 
If you actually measured the VD on 40m of 2.5 i would be surprised if it was much at all , certainly not 7 or 8 volts

But I suspect if you design the circuit using the OSG tabulated values it will suggest 4mm cable
 
If you’re running a new circuit out there, future proof it….

will you ever be using a lawnmower, leaf blower etc out there?

hottub? Has been known.

garden bar?

4mm minimum, gives some extra scope. Not a problem if your coming from CU.
 
If you’re running a new circuit out there, future proof it….

will you ever be using a lawnmower, leaf blower etc out there?

hottub? Has been known.

garden bar?

4mm minimum, gives some extra scope. Not a problem if your coming from CU.
Hot tub is going on separate circuit this circuit is solely for shed to run a small chest freezer and odd bit of power for battery charger
 
question is what earthing system, and is the shed liable to have any exreaneous parts e.g. a water supply run in condictive pipework. this would entail using a larger cable if PME/TNC-S.
 
If you’re running a new circuit out there, future proof it….

will you ever be using a lawnmower, leaf blower etc out there?

hottub? Has been known.

garden bar?

4mm minimum, gives some extra scope. Not a problem if your coming from CU.

question is what earthing system, and is the shed liable to have any exreaneous parts e.g. a water supply run in condictive pipework. this would entail using a larger cable if PME/TNC-S.
Earthing is tns system at main CU

No water supply in shed its a shed not a summerhouse the freezer is for falconry food
 
Right guys I have priced up both methods of installation straight form main CU and adding additional CU( garage board)in the shed and running lights and sockets off that

I think I will be adding additional CU in shed feeded by 10mm swa 2 core by my calculations the 10mm is more that capable of handling the current needed
 
Right guys I have priced up both methods of installation straight form main CU and adding additional CU( garage board)in the shed and running lights and sockets off that

I think I will be adding additional CU in shed feeded by 10mm swa 2 core by my calculations the 10mm is more that capable of handling the current needed
Show us your calculations then, you may get more help that way.
 
Last edited by a moderator:

Reply to Shed power in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Thank you for another very helpful response. Just to assure you we are saying the same thing, I was referring to the 2.5 on 20A radial which I now...
2
Replies
25
Views
2K
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top