Hi, a customer of mine phoned me the other night to say she had just touched the water inlet pipe to the shower and had a shock off it (she was in the shower at the time!)
I've been and looked at the job today and can't work out what is going on. I get a reading of 1 - 2 volts off the pipe whilest the shower is on. I also get this reading at different points on the pipework around the house.
Nothing when the shower is off. Surely this shouldn't happen but I wouldn't have thought she could get a shock off it....
I've check the bonding, its a TT system where a new c/unit has been run from the existing supply and the earth rod has been connected to the new box and then ran back to the old one. The installation is on a 100amp voltage controlled breaker and the shower circuit is on a 40amp mcb from the new box which has an RCD main switch. All pipework is bonded.
The loop reading from the shower is 181ohms.
Anyone got any ideas whats happening and why nothing is tripping....
cheers,
Justin
I've been and looked at the job today and can't work out what is going on. I get a reading of 1 - 2 volts off the pipe whilest the shower is on. I also get this reading at different points on the pipework around the house.
Nothing when the shower is off. Surely this shouldn't happen but I wouldn't have thought she could get a shock off it....
I've check the bonding, its a TT system where a new c/unit has been run from the existing supply and the earth rod has been connected to the new box and then ran back to the old one. The installation is on a 100amp voltage controlled breaker and the shower circuit is on a 40amp mcb from the new box which has an RCD main switch. All pipework is bonded.
The loop reading from the shower is 181ohms.
Anyone got any ideas whats happening and why nothing is tripping....
cheers,
Justin