ya isolate faulty circuit first -phase tester will do
Would rather not connect myself to the supply personally.
Phase testers belong in the bin.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss shocks off pipework... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
ya isolate faulty circuit first -phase tester will do
Well just got back...
For starters there was no main earth !!
Tried to get a ZE, but got some dodgy readings >55v and showing n-e. Old TT system.
Took all the fuses out and switched off, landlord is having to sort something out for tenants. One of tenants said they have been getting shocks for over a month and sometimes from the bath water So why did they only leave it until now to tell the landlord, crazy !! That place is a death trap.... sketchy original wall heaters in kitchen and bathroom, acient towel rail with wires hanging out in bathroom, the list goes on. And they've got 2 young kids in there. Also the old wylex CU is located outside the back door in a porch, but fully exposed to elements... all the fuses and screws were rusted in !
Another thing I noticed was the meter had been changed in FEB this year, surely they have to check for an earth! Or are they just a bunch of muppets on a price that are not actually proper sparkies ?
Whilst had cover off did a quick IR test L+N to E , on all the circuits to try and locate the internal fault/s. Ring, cooker and 2 x lighting circuits all these had less than 2m(Ohms).
Landlord is going to call local supplier and get put onto PME, should be ok flat upstairs has it. If they cant do this pretty soon will put an earth stake in, do CU change and find these faults.
So that it really, thanks for your advice anyway,
Sy