about the only thing i might use them for - a quick check on live metalwork

they don't see much duty
 
Last edited by a moderator:
Just to follow up....

DNO went out to have look at converting to PME yesterday, and could believe that meter man didnt report the state of current cutout and lack of earthing, apparently for Western Power they are suppose to ring this through !! DNO very appoligetic to customer and have arranged for PME upgrade this Monday instead of having to wait 6 weeks....
 
I had it before when tennants were getting shocks of the kitchen worktops,
not a belt but more of a nasty tingle

discovered no earth continuity on ringmain. rewire part of it back to point where there was an earth and it solved the problem

the problem only occured when the new dishwasher was on, I can only assume this dishwasher was dumping to earth and it had nowhere to go, so found its way to the damp kitchen worktops

anyway solved the problem so happy days+
 
Last edited by a moderator:
Well just got back...

For starters there was no main earth !!

Tried to get a ZE, but got some dodgy readings >55v and showing n-e. Old TT system.

Took all the fuses out and switched off, landlord is having to sort something out for tenants. One of tenants said they have been getting shocks for over a month and sometimes from the bath water :eek: So why did they only leave it until now to tell the landlord, crazy !! That place is a death trap.... sketchy original wall heaters in kitchen and bathroom, acient towel rail with wires hanging out in bathroom, the list goes on. And they've got 2 young kids in there. Also the old wylex CU is located outside the back door in a porch, but fully exposed to elements... all the fuses and screws were rusted in !

Another thing I noticed was the meter had been changed in FEB this year, surely they have to check for an earth! Or are they just a bunch of muppets on a price that are not actually proper sparkies ?

Whilst had cover off did a quick IR test L+N to E , on all the circuits to try and locate the internal fault/s. Ring, cooker and 2 x lighting circuits all these had less than 2m(Ohms).

Landlord is going to call local supplier and get put onto PME, should be ok flat upstairs has it. If they cant do this pretty soon will put an earth stake in, do CU change and find these faults.

So that it really, thanks for your advice anyway,

Sy

Hi

Not being funny, but when did the landlord last have a PIR done on this property? The installation surely didn't deteriate since the last tenants moved out?
 
God knows, don't think it's ever had one looking at state of it !!

He hasn't long brought the place, within the last year. And these are his first tenants and it's been let through an agent, who didnt even request a PIR !!
 

Reply to shocks off pipework... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K
  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top