vanessap

DIY
Joined
Aug 2, 2023
Messages
33
Reaction score
14
Location
Brighton
Hi Everyone,

I had a new consumer unit installed in December 2021, the electrician said that he had more testing to complete and would come back and said it could wait. My oven also began tripping on the same day, which he felt was a faulty oven.

I asked to schedule for a few months and unfortunately due to my mother’s Alzheimer’s care need access became difficult.

Things have calmed down and for the last few months I’ve been trying to arrange for the works to be completed and a certificate given. I met with the electrician / plumbing company last week who has been very difficult about providing most of the documentation; most of it has now been provided.

He has said that for the consumer unit installed at my home there is no continuity on a ring circuit and that he will not provide a completion certificate until it is addressed. Keeping in mind I have been asking him to explain the outcome and remedy any works.

I have contacted several other electricians who have said they can address this but cannot sign off the consumer unit and have advised that a completion certificate should have been provided noting the issue.

Please can I ask for your advice? Can a completion certificate be provided just noting the issues so someone else can come in?

Is no continuity in a ring circuit very dangerous?

The electrician is NICEIC registered, might you know if it is outlined that certification of works should be provided?

Surely if it’s not then unsafe work is not accounted for, if this fault is unsafe?

Thank you so much, in advance. Any advice would be really appreciated.

Many thanks,
Vanessa
 
Last edited by a moderator:
I wonder if there were singles in the white oval conduit in the first place...difficult to see.
But why on earth he didn't find a way to run behind the board and in from the back is beyond me.
 
I wonder if there were singles in the white oval conduit in the first place...difficult to see.
But why on earth he didn't find a way to run behind the board and in from the back is beyond me.
White oval conduit???

Oh my God! that's even worse!
 
BG boards always say bodger, I fitted two in my life when they first came out, never again, out of two boards and 4 RCD's 2 were faulty and didn't trip, even with the test button pressed and on top of that the lid was such a pain in the arse to get on I could have fitted a whole new board in the time it took me to get it on.

Edit: looks like they are still hard to get the lid on, the right hand screw isn't done up. Also what are singles doing in oval conduit anyway, that looks like someone has drilled through the cable/conduit and done a quick repair, maybe it was done after the mains unit was fitted, cant believe someone who fits consumer units has done that, even a cowboy.
 
BG boards always say bodger, I fitted two in my life when they first came out, never again, out of two boards and 4 RCD's 2 were faulty and didn't trip, even with the test button pressed and on top of that the lid was such a pain in the arse to get on I could have fitted a whole new board in the time it took me to get it on.

Edit: looks like they are still hard to get the lid on, the right hand screw isn't done up. Also what are singles doing in oval conduit anyway, that looks like someone has drilled through the cable/conduit and done a quick repair, maybe it was done after the mains unit was fitted, cant believe someone who fits consumer units has done that, even a cowboy.
"BG boards always say bodger, I have fitted two in my life". See how that reads😂😂
You can get oval to round adaptors and it can be used for singles.
 
"BG boards always say bodger, I have fitted two in my life". See how that reads😂😂
You can get oval to round adaptors and it can be used for singles.
That's before I knew they were a bodgers board. when they first come out in Screwfix they were £50 inc VAT and were very heavy so they felt like a decent board for the money, we got two as we had two jobs to do both requiring mains units. The first one when we tested it failed the RCD test so I nicked one out of the other board and took that back as faulty. when we fitted the replacement board on the second job that had a faulty RCD as well.

whenever I see one now that has recently been fitted they never have things like the grommet strip installed or a tails gland, they are all fitted crooked and a mess inside. I asked if they got many back as faulty, no they said, I'm probably the only one that tests RCD's then on boards like that.
 
I asked if they got many back as faulty, no they said, I'm probably the only one that tests RCD's then on boards like that.
Or, the two faulty ones you experienced came from the same batch…. The majority could be 99% perfect.

Any manufacturer could have a dodgy batch.

You can’t say other electricians don’t do tests just because of that


I remember several years ago, one particular size of one particular brand of mcb had a callback, and I had to check every static caravan we had sold in the previous 2 years, count them up, order replacements from each caravan manufacturer that used that make of mcb, swap them out and send the recalled ones back.
 
From a picture of the outside, I make these assumptions. (they may not be correct)

If it looks like "poo" from the outside, it is probably worse on the inside.
Single insulated cables outside the board are a big red flag to me.

Keep pushing the NICEIC for a resolution, I would be ashamed of myself even if I did that as a temporary lash up to get something up and running in the short term.
 
First of all the manufacturer of the dis board should not even come into this conversation. There is nothing wrong with the manufacturer, but as previously mentioned it’s the installer. The copex beggars belief and shows real initiative.. but it’s woeful. It looks harder to come up with that idea than infact, do it properly. As previously said, an eicr is usually carried out before the board is replaced to highlight any problems and they should be remedied prior to replacing. I wonder why he recommends a further eicr in 2 years?? I think the sticker reads that anyway? But this is the recommendation of the electrician based on the type and use of the installation as well as other factors. There are ways around your issues as people have mentioned. Get a registered electrician to carry out an eicr and remedy the problems. Ok… you may have to pay extra and you may say that the bodge job should be remedied by the cowboy that did it… but.. why would you want them back? Contacting the niceic is an option but, they will tell you to contact the electrician first and give them the opportunity to remedy the work. Let’s be honest…. Do they really care…they get the registration payment from said electrician annually so probably won’t care. Things like this happen all the time.. the amount of phone calls I get when customers say they have had an extension or a mains change and require it signing off and the sparky has done one is unreal. Thankfully most building control authorities are aware of this and will accept an eicr. As previously said.. an electrician will not sign off anyone else’s work… or I certainly wouldn’t. Hope you get sorted.
 
Hi Everyone,

Thank you all so so much for your thoughts and advice! I met with a really helpful NAPIT registered Electrician today, honestly his approach was almost like night and day in comparison. He visited both my mum's home and mine today:

At my mum's: He tested the junction box, he found the earth issue and discover that there were two spurs running off the cooker cable (sorry if I am saying thing incorrectly). He opened up the wooden flooring on the floor above to figure out how to rewire and bring a further cable down to make things safe and came up with a plan to remove all the trunking. Add new and chase new sockets and two light switches. He resolved the cable issue in the loft after testing and coupling them up differently.

At my home: He checked every single socket, changed out three faulty sockets, resolved the issue with the oven from this, narrowed the ring issue down to a cable under the floorboards in the living room.

I am a bit in awe of today.

He will be doing the works at my mum's home later this week.

He mentioned one thing that I hoped I could ask some advice on please. He had a look at the consumer unit that was installed at my home and explained that in the picture attached:

1. The cable thicknesses are incorrect as they are too small
2. The trunking has not been installed correctly

We agreed that he would resolve the fault with the ring continuity and that I would then request the final certificate from the previous electrician and he will provide me with a certificate for the works he has done.

I wanted to ask your thoughts on 1 and 2 in the image and if this is something that I should ask the first Electrician to make right before providing the consumer unit certificate they installed or if it would be okay to ask this Electrician. Or can the cable thicknesses stay as it is?

Thank you all so much for your time and advice, many many thanks, Vanessa
 

Attachments

  • [ElectriciansForums.net] Should a completion certificate always be given for works carried out please?
    IMG_1729.jpg
    367.6 KB · Views: 55
Glad you are getting somewhere. You don't want the first guy back.
1. The cable thicknesses are incorrect as they are too small
2. The trunking has not been installed correctly

We agreed that he would resolve the fault with the ring continuity and that I would then request the final certificate from the previous electrician and he will provide me with a certificate for the works he has done.

I wanted to ask your thoughts on 1 and 2 in the image and if this is something that I should ask the first Electrician to make right before providing the consumer unit certificate they installed or if it would be okay to ask this Electrician. Or can the cable thicknesses stay as it is?

1 - difficult to say, depends on a few factors like main fuse size and earthing type, but based on what you've said I'd be inclined to trust him to sort out anything he reckons needs doing. It doesn't look to be a big job to fit a new tail set. (I'm hopeless at judging cable sizes from photo's, someone else might be able to be more specific)

2 - He's definitely right, this is what a few of us were remarking on earlier in the thread. Depending on where that is going and what it's doing there are likely several better ways of installing that, probably without the flexible conduit at all.
 
Hi Everyone,

Thank you all so so much for your thoughts and advice! I met with a really helpful NAPIT registered Electrician today, honestly his approach was almost like night and day in comparison. He visited both my mum's home and mine today:

At my mum's: He tested the junction box, he found the earth issue and discover that there were two spurs running off the cooker cable (sorry if I am saying thing incorrectly). He opened up the wooden flooring on the floor above to figure out how to rewire and bring a further cable down to make things safe and came up with a plan to remove all the trunking. Add new and chase new sockets and two light switches. He resolved the cable issue in the loft after testing and coupling them up differently.

At my home: He checked every single socket, changed out three faulty sockets, resolved the issue with the oven from this, narrowed the ring issue down to a cable under the floorboards in the living room.

I am a bit in awe of today.

He will be doing the works at my mum's home later this week.

He mentioned one thing that I hoped I could ask some advice on please. He had a look at the consumer unit that was installed at my home and explained that in the picture attached:

1. The cable thicknesses are incorrect as they are too small
2. The trunking has not been installed correctly

We agreed that he would resolve the fault with the ring continuity and that I would then request the final certificate from the previous electrician and he will provide me with a certificate for the works he has done.

I wanted to ask your thoughts on 1 and 2 in the image and if this is something that I should ask the first Electrician to make right before providing the consumer unit certificate they installed or if it would be okay to ask this Electrician. Or can the cable thicknesses stay as it is?

Thank you all so much for your time and advice, many many thanks, Vanessa
It's good to see a bit of positive news.
It seems you have someone who knows what they're doing involved.
Regarding I and 2 in the image, go with the advice of your electrician on site....he's seen things first hand.
Don't presume all NICEIC registered are bad and NAPIT the opposite. Both are money making organisations with a purpose to serve. Although standards have declined, in general, it seems you picked a bad un, initially.
Was it a cheap installation?
Hope for a satisfactory conclusion.

PS. That pvc conduit is a true shocker.......both ends.
Wiska box and 2 glands or white pvc conduit, easy to sort.
Judging cable size from photos is pure guesswork.
 
Last edited:
I'd be looking at where the conduit goes. It might be to a socket underneath, in which case a new length of cable all the way to the CU, entering behind it might be the best option. But from the sounds of it the latest guy knows his stuff and I would guess he'll assess things and give some options.
 

Reply to Should a completion certificate always be given for works carried out please? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I’d say yes go for it.
2
Replies
18
Views
2K
Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views