youngsparky

Hi all,
My girlfriends mum shower has gone faulty she is planning on a new one. Done some investigating and it's a 9.8 kw on a 6mm on a 32a breaker. Why hasn't the fuse bin blowing?
I havent done any cable calcs as of yet.
Any ideas just curious?
Cheers
 
Mcb's have a fusing ration of between 1.2 and 1.6, so dependant on its type, age etc etc it could take anything between 38.4 and 51 amps to trip it, the shower will pull around 40-42 amps depending on the supply voltage and VD, cable calcs wont really tell you a lot as apart from VD, there is nothing in there that will affect the current drawn, cable calcs are all about the current carrying capacity of the cable.

however, the cable is undersized for the size of the shower so its probably a good job its only a 32a breaker
 
Hi all,
My girlfriends mum shower has gone faulty she is planning on a new one. Done some investigating and it's a 9.8 kw on a 6mm on a 32a breaker. Why hasn't the fuse bin blowing?
I havent done any cable calcs as of yet.
Any ideas just curious?
Cheers

It's a short duration overload, my daughter could make it trip with a long duration overload!
 
I'm wondering whether or not it's on a mains water feed or a header tank. I've seen plenty of old showers burnt out due to inadequate water pressure after they've been fitted by a less than concientious plumber (or spark!). New showers will normally not attempt to heat the water if there is insufficient pressure, so if you fit a new one and it won't get warm you may have the culprit.
Just a thought.
 
Last edited by a moderator:
.

however, the cable is undersized for the size of the shower so its probably a good job its only a 32a breaker


Possibly not - clipped direct it can be up to 47A. As IQ said it is probs fine for showers of 15min duration but the mcb could trip if the whole family want a go one after the other :)
 
Possibly not - clipped direct it can be up to 47A. As IQ said it is probs fine for showers of 15min duration but the mcb could trip if the whole family want a go one after the other :)

Very true!!

However when was the last time we seen a shower cable clipped direct,with no de-ration factors applied. The normally always run through Walls, voids and insulation at some point.
 
Run in masonry still counts as clipped direct. I came across the very same thing some time ago and thought 'hold on this can't be right' but when i sat down with the brb it turned out ok and the shower had been working ok for years. I could have put it on a bigger mcb but thought why fix it if it ain't broke lol
 
Run in masonry still counts as clipped direct. I came across the very same thing some time ago and thought 'hold on this can't be right' but when i sat down with the brb it turned out ok and the shower had been working ok for years. I could have put it on a bigger mcb but thought why fix it if it ain't broke lol

Yea I know that chased is the same method, I'm just always wary of 10kw showers on 6mm2 as a shower cable almost always runs into insulation etc etc

The op is by his name still learning hence I made the comment of the mcb holding because of it's fusing factor and was saying it was probably a good job that it was on a 32a as if it was a 40a then the cable would possibly be working at the top of it's tolerances

Having said that the diy'ers in the slums round here install 10kw showers on cooker flex so it's all good
 
before condemning the 6mm. i would 1. ensure it wasn't buried in insulation. 2 clamp meter the cuurent drawn. bet it will be under 40A, nearer 35A.
 

Reply to Shower cable breaker question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

As a trainee, one of the things I've tried to focus on to deepen my interest in the world of electrics, is the space for creativity. I've...
Replies
0
Views
416
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top