Shower cable breaker question | Page 2 | on ElectriciansForums

Discuss Shower cable breaker question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

And from the earth term in the shower unit along the hose to the shower head just to be sure
 
used to be on the old rubber cable and horsehair & lime plaster. modern cable/plaster no problem, but capping is advisable due to plasterers being let loose with sharp tools.
 
can be metal or plastic - just a bit of protection for when it is plastered. Also gives the theoretical chance that you could always pull a new length of cable in :rolleyes:
 
6mm2 will take alot more than 47A

And there lie's the problem with DIYers We have be trained from the very start of our training, that cables need de-rating according to the environments in which the cable is installed. Whereas in reality the cable can and will draw far more than than it's de-rated calculated value. In this situation as regarding a shower installation, the over current will only generally be drawn for short periods of time... So the cable is probably not being stressed to extremes and the 32A MCB isn't receiving sufficient time to trip the over current section within the MCB... So to the householder/DIY'er
everything is Sweet!!! AS has been stated, the problems come when the usage changes, like when children become teenagers, especially of the female variety (though there are quite a few male teenagers that are more like tarts in the bathroom...lol!!)

Is the installation alright then?? ...No of course it's not, We know the very real dangers of these situations, but you try telling DIY Joe that after years of reliable service that he got it all wrong!!! It's the same old story, and your looked at as though your just wanting to make an extra few quid at his expense and for no obvious benifit!!!!....
 
Last edited by a moderator:
Thanks lads this discussion has helped me with a similar problem ;

neutral at the back of the double pole switch has melted insulation & the back of the switch. 10 mt run of 6mm to a 9kw shower on a 32a mcb. So gonna replace the cable with 10mm t+e, replace double pole switch & run from a single shower rcd.

So does it need tested too?

Thanks for the input ;-)
 
No the new installation from the shower RCD to the shower itself.
Continuity.
Insulation resistance tests.
Zs test.
RCD test.
And test Ze at origin so you know you gotta a good earth.
And it's notifiable. :D
 

Reply to Shower cable breaker question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

As a trainee, one of the things I've tried to focus on to deepen my interest in the world of electrics, is the space for creativity. I've...
Replies
0
Views
416
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top