melted neutral? could that be loose connection rather than the cable being too small?
Absolutely, a 9Kw load on 10 Metres of 6.0mm would not melt the insulation.
melted neutral? could that be loose connection rather than the cable being too small?
If your unsure wether to re run the cable or tighten connection. Do what you think is safest.
I always like to leave a job knowing it's the safest it could ever be
That's what I thought. New DP switch, re-terminate, test. leave.
design current 39 amps.
6mm clipped direct 47amps