Was reading an older thread and dont have any books to hand, but basically.

If a cable for a 10kw shower is to be run, the current drawn would be 43.4 A.

So if 6mm cable was appropriate for say 70% of the run that was clipped direct, but not suitable for 30% of the run due to de-rating factors, as it would be covered by insulation . Could you size up to a 10mm cable just before the cable hit the insulation part of the run, the drop back to 6mm after the insulation where it may be clipped direct again.

I would like to note that this a hypothetical question, and the thought behind it was that if you had a long run then being able to buy only 30% of the run in 10mm would save you monies on cables.

Also (on a separate note) with gu10 firerated lights is there a recommended clearance of insulation from around them i.e. in a loft where the lights come up from ceiling below, as I presume you would want as much insulation to remain as possible.

Hope that all makes sense, thanks.
 
Stepping up, or down, depends on which way you are looking at it :)
Personally, I wouldn't change cable size to allow for derating through a small section. Remember, a cable should be selected appropriately for all factors that affect it. If you take this hypothesis to the nth degree you could end up with several connections in one length.
 
Stepping up, or down, depends on which way you are looking at it :)
Personally, I wouldn't change cable size to allow for derating through a small section. Remember, a cable should be selected appropriately for all factors that affect it. If you take this hypothesis to the nth degree you could end up with several connections in one length.

Maybe on an outside lighting circuit, for example, wired in, say, 6.00mm because of volt drop, some of the further points could be wired in smaller...?
 
As already mentioned it could be done, but could doesn't equate to should. The only time I would do something like that would be the run to and from the isolator. So you may have 6mm to the isolator and 10mm from the isolator to the shower as it runs through an insulated stud wall. Doing it that way though is more about convenience for running the cable and making it off than the cost of cable.
 
Maybe on an outside lighting circuit, for example, wired in, say, 6.00mm because of volt drop, some of the further points could be wired in smaller...?

Virtually every street/road lighting arrangement is installed this way. as the load get's lighter the supply cable size is reduced. Lucy and other street lighting protection equipment suppliers, have standard post equipment that facilitates this arrangement....
 
Virtually every street/road lighting arrangement is installed this way. as the load get's lighter the supply cable size is reduced. Lucy and other street lighting protection equipment suppliers, have standard post equipment that facilitates this arrangement....

Exactly my point.
 
50m 10mm T+E ÂŁ170

10m 10mm T+E ÂŁ35
50m 6mm T+E ÂŁ 75

This is just a question i wondered to myself, and so the length of runs could vary but as long as it conformed to 7671 and the joint in cable was necessary due to derating, then on a '50m' run you can save ÂŁ60 or 1/3 of the cost of cable by this method. I would again like to stress I am not contemplating this as an installation I was just wondering and thought someone may be able to satisfy my curiosity.

Its not that simple. Are we pricing for a junction box as well. How long would it take you to mount the box and make it off.
 
Virtually every street/road lighting arrangement is installed this way. as the load get's lighter the supply cable size is reduced. Lucy and other street lighting protection equipment suppliers, have standard post equipment that facilitates this arrangement....

My apologies. I thought we were hypothesising about a standard domestic situation.
I will get my coat... :waving:
 
Think your referring to stepping down a cable size!! The bigger the cable the better, except for your, or your clients bank balance!! lol!!!

Getting back to the topic, yes you can do it this way, but no self respecting spark would do so, your just adding unnecessary joints and weakness into a circuit. On top of that, it's going to probably work out cheaper to run the circuit as it should be done, in the lager cable size, when considering the overall costs...
quite right eng...the voice of sense....
 
Ok, so basically you could, but whether you should or would is different. That is fine, as this isnt a real situation there is no need to panic.
Also with regards to the junction box costing extra money and time, surely pulling a 10mm cable over a '50m' run (with v.d excluded and not being taken into account) would be more tedious than pulling a 6mm cable...

Nonetheless my question has been answered and thanks for that !

.....one more thing ha, if you were to design a circuit with all things considered and no insulation around any cable, then mr ecosulation man comes and dumps a crap load of insulation on your cable thereby severely underrating it and a fire starts would he be solely liable and responsible?
 

Reply to Shower circuit 10mm in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
333
  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
920

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top