Was reading an older thread and dont have any books to hand, but basically.
If a cable for a 10kw shower is to be run, the current drawn would be 43.4 A.
So if 6mm cable was appropriate for say 70% of the run that was clipped direct, but not suitable for 30% of the run due to de-rating factors, as it would be covered by insulation . Could you size up to a 10mm cable just before the cable hit the insulation part of the run, the drop back to 6mm after the insulation where it may be clipped direct again.
I would like to note that this a hypothetical question, and the thought behind it was that if you had a long run then being able to buy only 30% of the run in 10mm would save you monies on cables.
Also (on a separate note) with gu10 firerated lights is there a recommended clearance of insulation from around them i.e. in a loft where the lights come up from ceiling below, as I presume you would want as much insulation to remain as possible.
Hope that all makes sense, thanks.
If a cable for a 10kw shower is to be run, the current drawn would be 43.4 A.
So if 6mm cable was appropriate for say 70% of the run that was clipped direct, but not suitable for 30% of the run due to de-rating factors, as it would be covered by insulation . Could you size up to a 10mm cable just before the cable hit the insulation part of the run, the drop back to 6mm after the insulation where it may be clipped direct again.
I would like to note that this a hypothetical question, and the thought behind it was that if you had a long run then being able to buy only 30% of the run in 10mm would save you monies on cables.
Also (on a separate note) with gu10 firerated lights is there a recommended clearance of insulation from around them i.e. in a loft where the lights come up from ceiling below, as I presume you would want as much insulation to remain as possible.
Hope that all makes sense, thanks.