Was reading an older thread and dont have any books to hand, but basically.

If a cable for a 10kw shower is to be run, the current drawn would be 43.4 A.

So if 6mm cable was appropriate for say 70% of the run that was clipped direct, but not suitable for 30% of the run due to de-rating factors, as it would be covered by insulation . Could you size up to a 10mm cable just before the cable hit the insulation part of the run, the drop back to 6mm after the insulation where it may be clipped direct again.

I would like to note that this a hypothetical question, and the thought behind it was that if you had a long run then being able to buy only 30% of the run in 10mm would save you monies on cables.

Also (on a separate note) with gu10 firerated lights is there a recommended clearance of insulation from around them i.e. in a loft where the lights come up from ceiling below, as I presume you would want as much insulation to remain as possible.

Hope that all makes sense, thanks.
 
ultinator;579554 then mr ecosulation man comes and dumps a crap load of insulation on your cable thereby severely underrating it and a fire starts would he be solely liable and responsible?[/QUOTE said:
Imho yes. You have designed properly and installed, inspected and tested to 7671 and have copies of the paperwork to prove it. Mr Insulation comes along with his ignorance and screws everything up.
I'd say that ignorance of our regs is no excuse, after all we're supposed to be aware of all building regs so why shouldn't he?
 
.....one more thing ha, if you were to design a circuit with all things considered and no insulation around any cable, then mr ecosulation man comes and dumps a crap load of insulation on your cable thereby severely underrating it and a fire starts would he be solely liable and responsible?

Normally I would say, if your install complies at the time you did it, no problem, you can't be held responsible for what happens to it in the future.
But...if you were laying cables in an uninsulated attic on the ceiling below (you know what I mean!), for example, there is a good chance that cables would be covered over in the near future, especially with these free loft insulation offers going. Had mine done for freebies a couple of years ago.
 
quite right. would he pile a foot of fibreglass on top of the kitchen hob, or cram it roung the C/H boiler. ... NO. so why should the muppet treat our installations with such disrespect.
 
If you can reasonably foresee a situation where thermal insulation could compromise the integrity of your installation, then you should take the appropriate course of action to protect the electrical system.
 
If you can reasonably foresee a situation where thermal insulation could compromise the integrity of your installation, then you should take the appropriate course of action to protect the electrical system.
good thinking. a 12 bore in the attic with a piece of string attached to the hatch. that should sort it.
 
then again, in a house less than 40 yrars old, it would probably collapse the roof trusses,, explode the water tank that the kind plumber has placed in the only space that you can crawl through, bonus free sprinkler system.
 

Reply to Shower circuit 10mm in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
333
  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
920

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top