Argument at work!
on an EICR its common to find a 9.5kW shower wired in 6.0mm T/E with a 40 amp MCB.
obviously a code 2 unless short run and clipped direct?
Our argument is whether to down rate MCB to a 32amp or rewire the circuit in 10mm?
I say ok to down rate the MCB as
cable is 32amp IEE say must take 1.45 times rating for 1 hour and not exceed 60 deg C also 32amp mcb will take this current
others say rewire shower in 10mm, I would agree if new install, but on an EICR it would reduce the coding to a C3 and I would note " Circuit derated and a shower rewire desirable?