Shower supply, ever needed additional earth cable. | Page 2 | on ElectriciansForums

Discuss Shower supply, ever needed additional earth cable. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

It is not likely the cpc was inadequate the only time this may apply was when 2.5 cables had 1.0 cpcs on BS3036 30A fuses.
 
was in 16th, all electrical equipment in bathroom supplementary bonded to each other like spaghetti. ( except the metal windows and bog flush. these were the preserve of D.W. cock something.
 
It is not defined as "supplementary equipotential protective bonding" in BS7671, so I'm unclear as to what point you were trying to make.
Sorry.
Supplementary protective equipotential bonding.

Point is this:
The 16th allowed supplementary bonding to be used where a low enough value of Zs for ADS could not be achieved.
 
Last edited by a moderator:
Point is this:
The 16th allowed supplementary bonding to be used where a low enough value of Zs for ADS could not be achieved.
Yes it did. And so did the 17th. My point was that this was not there to reduce the Zs but to maintain the touch voltage at a safe level until disconnection occurred (even though this would not be within the prescribed disconnection times).

It obviously might result in an improved Zs but this most certainly is not the purpose of it, but merely incidental.
 
I await @westward10 reading guidancen with interest. I think this requirement was killed by RCD's which changed the game. Bonding in the 16th was so misunderstood - people bonded everything, some plumbers still do it today! However working somewhere that has no RCD protection (given the date of install) may require it (not to be removed).
 

Reply to Shower supply, ever needed additional earth cable. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
632

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top