I'm putting in an electric shower (7kW), which will be protected (and clearly labelled as being for that purpose) by a 30mA 2-pole RCD + 32A MCB (garage/shower type connection unit - no main switch in it, just the RCD & MCB) going outside the bathroom in the airing cupboard at an easily accessible height.
Can anyone think of a reason why in addition to the RCD a dedicated shower switch (pull cord or 'cooker type' or whatever) is *required* by the regs? I've been having a read and can't immediately see anything. Section 701 (bath/shower location) doesn't seem to help. Section 537 (isolation/switching) is relaxed about an RCD being used for isolation (table 53.4)...can be secured in open position...contact positions are indicated...inadvertant closure prevented (unit has a cover)....537.3.2.2 says "shall require manual operation". Hmmm. Does it mean it must *only* be manually operated? Obviously the RCD provides ADS however it only automatically disconnects, never reconnects...
Thoughts? Cheers guys.
Can anyone think of a reason why in addition to the RCD a dedicated shower switch (pull cord or 'cooker type' or whatever) is *required* by the regs? I've been having a read and can't immediately see anything. Section 701 (bath/shower location) doesn't seem to help. Section 537 (isolation/switching) is relaxed about an RCD being used for isolation (table 53.4)...can be secured in open position...contact positions are indicated...inadvertant closure prevented (unit has a cover)....537.3.2.2 says "shall require manual operation". Hmmm. Does it mean it must *only* be manually operated? Obviously the RCD provides ADS however it only automatically disconnects, never reconnects...