If you do a board change and the installation only has 6mm2 earth cable to its gas and water is it a requirement of the regulations that you change it for 10mm2? Or can you recommend its upgrade but if its declined just leave it?

Help appreciated;)
 
If you do a board change and the installation only has 6mm2 earth cable to its gas and water is it a requirement of the regulations that you change it for 10mm2? Or can you recommend its upgrade but if its declined just leave it?

Help appreciated;)

well 130-07-01 (16th edition), is now 130.8.1 in the 17th, and that says that the earthing and bonding must be adequate, but 130.8.1 now also says 'if neccesary for the protective measure applied for safety', and assuming your using ADS for protection, then i would say yes.

Additionally, NOT upgrading the main protective bonding, would mean, for example, that you would have to use supplementary in the bathroom (should you need to work on any circuits in there)

to be honest, the regs doesnt specifically answer this question )in my opinion) but obviously, it would be better upgraded
 

Reply to Size of equipotential bonding???????? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top