How do you know what size of earth wire to use from the bango to earth terminal in a DB, when using say:

25mm 4-core swa sub main feeding a DB. (L1, l2 l3 and neutral, armour used as cpc).

I would gland, with a bango and choose a size half of the phase size, so 16mm earth lead i would use. Is this ok, or OTT!?

so if 4mm2 armoured is used, I would use a fly lead of 2.5mm earth? Cant be wrong can it?

Cheers guys
 
543.1.4 says when not using adiabatic equation to calculate then use table 54.7, table states where line conductor is equal to or less than 16mm then protective conductor should be the same size.
 
OP using 25mm 4 core with SWA as CPC
so CPC = S/2 if same material but it isn't it is steel
So you need to check CSa of SWA is compliant IE equivalent to 16mm copper
Assuming SWA CSA is compliant then fly lead should be 25/2 = 12.5 mm
No 12.5 cable so in this case 16mm copper fly lead is BS7671 compliant.
for 4mm with SWA as CPC fly lead 4mm is SWa compliant
for 4mm with core as CPC it is already 4mm so fly lead 4mm
 
Hi,

I have just been looking through GN8, GN8 9.3.5 and it says where the amouring is not used as a cpc it becomes an exposed conductive part (which requires earthing), but does not give any details as regards the banjo cpc/earth tail sizing.

Looking at GN8 table 8.1 supplementary bonding for exposed conductive parts give the usual 'where not protected mechanically min 4mm' etc.

The situation is not helped by GN8 not up to 17th ed. (this is the latest version).
I hear what other posters are saying re: sizing the same as cpc, but can anybody point to the relevant regs and guidance on this point ?, as I assumed (rightly or wrongly) the banjo tail would be 4mm, again when the armouring is not used as a cpc, for example where glanding the armoured cable into say a metal DB or metal Isolator etc.

TIA
 
Last edited:
If you are NOT using the Armour as the CPC then you must be using a separate CPC that must be sized correctly
It follows that the Armour is an exposed part of the circuit and must be connected to earth by a CPC so the banjo fly lead = same size as the CPC what ever that is. EG: CPC = 2.5 fly lead 2.5, CPC 4mm fly lead 4mm and so on To size the CPC use Adiabatic formula or table in Regs
 
Hi Platty,

The situation I had in mind, is when using armoured cable say 3 core for SP+E, or 5 core for TP+N+E, or 4 core for TP+E, it follows your cpc will be the same size as the line conductors as it is one of the cores, so this bit is straight forward.

Are you saying the banjo earth tail in this case has got to be the same size as the cpc ? or S/2 or by adiabatic ?, again this is when the armour is not used as the cpc, but is still required to be earthed, or is the exposed conductive part just extraneous as I cannot see a definite reg relating to this.

I was just asking out of interest, as the information seems a bit vague, I have seen earth tails in 2.5mm and in 4mm etc. , connected to the banjos, although I never took that much notice of what size the cpc/line conductors were, and whenever I have fitted them I have just used the same size as the cpc.

Any info./clarification welcome
 
Last edited:

Reply to Sizing bango earth fly lead in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
642
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top