Been 2nd fixing today, which i've not done for many years. I've noticed that both Volex 13A twin & single sockets have 2 x earth terminals. Is that now standard? I thought that requirement was only applied to sockets that served a lot of IT equipment. Even years ago i would sleeve the earths separately, but then into one terminal. Is there any electrical reason for the change? Thanks
 
Ring circuits, by their design, provide duplication of all conductors, including the protective conductor unless this is formed by metallic conduit and/or trunking. Regulation 543.7.1.104 requires that each protective conductor is terminated separately at each connection point; the regulation also requires that each wiring accessory has two separate earth terminals. At socket-outlets, this is a very easy requirement to meet – simply select accessories with dual earth terminals.
 
As far as I can recall, the requirement is for a CPC with a minimum CSA of 4mm, or for there to be 2 CPCs both of which must satisfy the requirements to be considered as a CPC.
RFCs are effectively a circuit with conductors run in parallel so in a standard RFC run in 2.5mm T&E the conductor sizes can be considered as 4mm line, 4mm neutral but only 3mm CPC.
3mm as I am sure you are aware, is less than the 4mm required.
Some people say that because it's 2 conductors, it is therefore 2 CPCs.
That's ok, as long as both of the conductors would satisfy the requirements to be considered as CPCs.
When RFCs are run in singles, all of the conductors are usually the same CSA, so if the CSA of the CPC is 2.5mm, then when doubled, we have 5mm which is greater than the minimum 4mm required.
 
Last edited by a moderator:
Ring circuits, by their design, provide duplication of all conductors, including the protective conductor ..................

It's not though, is it?!?! The conductors carry differing currents along their lengths.

Also, if you whip out a section of the ring (or get a break :) ), what do you get????
Two undersized Radials!

Yes i am sure! You may have two ends but its two ends of the same cpc! There aren't two seperate circuit protective conductors!

I completely agree! :)
 
Last edited by a moderator:
i was always taught one cpc from each leg into each terminal then link between the two so not relying on the socket as the link, that way if one comes loose there is still another terminated and socket is still protected rather than losing both earths.
 
Those few pence per socket add up when you are mass producing.

How many times have manufacturers tried to save a few pence that have ended up costing them millions
There are so many factors to consider in mass production a few pence for an extra terminal is only one of them

i was always taught one cpc from each leg into each terminal then link between the two so not relying on the socket as the link, that way if one comes loose there is still another terminated and socket is still protected rather than losing both earths.

I've done that a few times to get round a resistance problem on the socket link
 
How many times have manufacturers tried to save a few pence that have ended up costing them millions
There are so many factors to consider in mass production a few pence for an extra terminal is only one of them



I've done that a few times to get round a resistance problem on the socket link
why would you do that except on it installations?

you want the conductors together or your just adding more resistance for no reason
 
If when testing an RFC you discover the CPC is not continuous, what code would you apply and why?

firstly , why would i bother giving a reply to that question when you were unable to answer in your own words why you would issue a C2 for 3.5mtr tails in yesterdays meter thread ?

secondly , your question has no relevence to the statement i made above.
 
firstly , why would i bother giving a reply to that question when you were unable to answer in your own words why you would issue a C2 for 3.5mtr tails in yesterdays meter thread ?

secondly , your question has no relevence to the statement i made above.

I have answered that question.
Here is the answer again:
It does not comply with BS7671 and it is potentially dangerous.

Why is it not relevant?
You are suggesting that an RFC if split is two Radials, therefore there are two CPCs.
If that's the case then a discontinuous CPC on an RFC should have no code.
 
I have answered that question.
Here is the answer again:
It does not comply with BS7671 and it is potentially dangerous.

Why is it not relevant?
You are suggesting that an RFC if split is two Radials, therefore there are two CPCs.
If that's the case then a discontinuous CPC on an RFC should have no code.

your original answer consisted of nothing more than a link to a meter operators code of practice , which is completely irrelevent with regards to an inspection conducted to bs7671

and youre still not making it clear how we go from no code for 3mtr tails to C2 for 3.5mtr and a discription of the hazard posed to incur such a code.

yes , i said a rfc split is 2 radials with 2 cpcs.

the reason you would issue a defect code for a break in cpc continuity on a rfc is because a circuit designed to operate as a rfc is no longer functioning in the manner that it was originally intended , which in no way contradicts my statement that a split ring contains 2 cpc's.
 
I'm not sure where the 4mm CPC comes into play other than the flex from the sockets above 16a.
the min size of CPC for the two individual conductors on a ring final circuit is 1.5mm

My maths must not be upto much if there is only one CPC in a ring circuit...
 
The 4mm requirement is for where high integrity earthing is required.
I believe the minimum CSA is 10mm if not copper, and 4mm if copper.
I don't know about your maths.
As for there being 2 CPCs in a RFC, fine, I imagine that they both connect to every point served on the circuit as per the requirements of BS7671?
As I said earlier an RFC is effectively a circuit supplied using parallel conductors.
Unless the combined CSA of the CPC conductors is greater than 4mm, a separate CPC will be required.
That separate CPC is required to be such that fulfills the requirements that pertain to CPCs.
In other words, you can't just run in a 1mm conductor to take the total CSA of the CPC conductors to 4mm.
If the RFC is wired in singles and the CPC conductors are 2.5mm, then the combined CSA of the two CPC conductors is 5mm, which exceeds the 4mm minimum, and another separate CPC is not required.
 
your original answer consisted of nothing more than a link to a meter operators code of practice , which is completely irrelevent with regards to an inspection conducted to bs7671

and youre still not making it clear how we go from no code for 3mtr tails to C2 for 3.5mtr and a discription of the hazard posed to incur such a code.

yes , i said a rfc split is 2 radials with 2 cpcs.

the reason you would issue a defect code for a break in cpc continuity on a rfc is because a circuit designed to operate as a rfc is no longer functioning in the manner that it was originally intended , which in no way contradicts my statement that a split ring contains 2 cpc's.
Not stating that your statement is contradicted.
I did ask what code you apply.
I would also remind you that BS7671 only requires us to comment and code instances which may give rise to danger. The're is no requirement to make observations or apply codes to instances that do not give rise to danger.

So to repeat my question:
What code and why would you apply to a discontinuous CPC in a RFC?
 

Reply to skts x 2 earth terminals in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
745
Thanks Brian. I'll keep doing it then, no harm I suppose. I am lucky in that being DIY, I have the luxury of time when it comes to this kind of...
Replies
4
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top