skts x 2 earth terminals | Page 5 | on ElectriciansForums
Discuss skts x 2 earth terminals in the UK Electrical Forum area at ElectriciansForums.net
England
Been 2nd fixing today, which i've not done for many years. I've noticed that both Volex 13A twin & single sockets have 2 x earth terminals. Is that now standard? I thought that requirement was only applied to sockets that served a lot of IT equipment. Even years ago i would sleeve the earths separately, but then into one terminal. Is there any electrical reason for the change? Thanks
C2 , as recommended in the ESC EICR coding guide , for the reason i gave in the last sentence of my previous post.
I wish your answers were as clear and concise spin , the round the houses, ambiguous waffle that you fill your posts with doesnt half make for a tedious debate.
Spin you will have to point me in the direction of this 4mm min size for CPC? As I have looked in guidance notes 1 & 8 and there is no mention of this.
if you have a copy of onsite guide to hand, for very basic reference pages 78, 79.
I'm still learning how to debate points, and explain myself so as there can be no misunderstanding.
Getting back to the point under debate, you and obviously the ESC/NICEIC consider a discontinuous CPC in a RFC to be a potential danger.
BS7671 requires that if one of the CPCs fails, then the other CPC should be capable of taking over.
It's no good having two CPCs, neither of which comply with the Regulations.
That is relying on section II being fullfilled as that also falls under section 543.
Section II:
A single copper protective conductor having a cross sectional area of not less than 4mm2, complying with the requirements of 543.2 543.4, the protective conductor being enclosed to provide additional protection against mechanical damage, for example, within flexible conduit.
III
Two individual protective conductors each complying with section 543, the ends being terminated independently
Are we talking about high integrity earthing here where IT equipment and the like are the main circuit loading? I can't think of any other reason why the ends would need to be terminated independently??
Section II:
No, the header says "...with one or more of the following" page 166 of your 7671
part ii is for a single conductor.
the size of CPC is calculated or selected as per section 543
I did think the picture on page 79 osg would have made it a bit easier but how wrong was I lol.
Yes the image makes it perfectly clear, that's how you terminate the CPC for high integrity circuits.
This whole thread has been about using single or dual terminals for standard circuits there is no disputing using them for a circuit with high protective conductor currents.
Im not 100% sure what your getting at?
Me & Spin were discussing CPC's for final circuits with sockets that may have currents that exceed 10mA.
Reply to skts x 2 earth terminals in the UK Electrical Forum area at ElectriciansForums.net
Thanks Brian. I'll keep doing it then, no harm I suppose. I am lucky in that being DIY, I have the luxury of time when it comes to this kind of...
Recommended Sponsor News
Hi everyone,