543.3.201 requires bare protective conductors up to and including 6mm which are incorporated within a sheathed cable to be protected by insulating sleeving in accordance with BS EN 60684 where the sheath is removed at joints am determinations.
Sleeving for cable for Ident is Manufactured to BS EN50525 see aslo Reg 514.4.2
The sheath hasn't been removed thought mate is was never there in the first place.
Is this the sort of debate you envisaged Charlie between basically 3 knowledgeable Electricians???????
Haha not sure really..
I just thought that we also used certain types of sleeving to also provide insulation.
I opened up a panel a while back and all the CPCs were bare.. Some were not terminated so I also got a few tingles from them.. The sleeving would also protect the bare wires from coming into contact with busbars?
Good that I managed to get a debate out of such a very basic question from the op though :)
When the cpc sleeving first appeared, it was practice or common practice that IF THE ACCESSORY wasn't prone to regular removal, then sleeving was not required, or that's how it was interoperated by the outfit I worked for, mind you that was before many of the younger generation, had any inkling of joining the electrical industry. So many CUs DBs didn't use cpc sleeving.
Reply to Sleeving 3 phase cable to single phase cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
All of the information for MG stuff is freely available from Schneider
davesparks
Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...