What I think your saying is that you would put the incoming tails through a contactor, that is assuming that the DB is a dedicated board for power, there is no evidence of that, in fact as it seems to be a small industrial unit the chances are that is is a combined board including lights
Agree if it is a designated board just for the 3 phase sockets, it may pay you to wire the tails through a contactor, only down side to that is you limit what can be added to the board at a later date.
Also you would need a far larger capacity contactor that one just feeding a Ring Main to the 3 phase sockets.
Also the client may not take too kindly to the emrgency stop being activated, that also kills the 13amp sockets if they are feeding an office.
Also just as a note the contactor would have to a 4 pole as emergency switching needs to isolate all LIVE conductors.