Its a joinery shop only manned by 1-2 people.
therefore probably only 2 machines used at any one time.
thanks for your help
Hi All,
I am due to wire a small industrial unit, they want 14 double sockets 10x 3phase 16 amp sockets, a new mains board and all wired in swa cable on metal tray.
The gear will cost around ÂŁ1000.00. was thinking around a week to install.
can anyone give me a ball park figure for the whole job?
Ive to test and certify all work also. many thanks
NO, PLEASE, DO NOT RUN A 3ph RING.
YOU WILL NOT comply with legislation.
Listen to Engineer54.
You need to run individual supplies to each machine to comply with both 7671 & other statutory regs.
There are also considerations in 7671 you may not think about, check the brb carefully to ensure compliance in wood working premises.
It is easy to install a non compliant installation without realising!
Would you mind quoting the regulations in BS 7671 that says you can't run 3 phase sockets in a Ring.Would you mind quoting the regulations in BS 7671 that says you can't run 3 phase sockets in a Ring.
Hi All,
I am due to wire a small industrial unit, they want 14 double sockets 10x 3phase 16 amp sockets, a new mains board and all wired in swa cable on metal tray.
The gear will cost around ÂŁ1000.00. was thinking around a week to install.
can anyone give me a ball park figure for the whole job?
Ive to test and certify all work also. many thanks
NO, PLEASE, DO NOT RUN A 3ph RING.
YOU WILL NOT comply with legislation.
Listen to Engineer54.
You need to run individual supplies to each machine to comply with both 7671 & other statutory regs.
There are also considerations in 7671 you may not think about, check the brb carefully to ensure compliance in wood working premises.
It is easy to install a non compliant installation without realising!
Would you mind quoting the regulations in BS 7671 that says you can't run 3 phase sockets in a Ring.
As far as i'm aware there is no regulation, in fact rings are permissable for just about any size of circuit and certainly quite common in installations such as these!