Please tell me you are fitting a switch fuse between the 100amp intake and the shower. If the switch fuse is within close proximity to the 100amp service fuse then I would say its fine but its not if you are going to feed the 6mm straight off the service fuse and not protect it.
 
Agreed, told the firm I do some work for to get 16mm2 tails for our solar Pv boards. Answer was no it needs to be 25mm!!
 
usually in those cases, the undersized tails feed a switch/fuse or small CU which is fused down within a few inches of the henleys, so theoretically those undersized tails can't be overloaded.

AS the above, as telectrix states if there is a switched fuse or small CU installed within a few inches of a cut out then the tails cannot be overloaded, however the tails are still only protected by the main cut out, which is not correct.

All fuses should have a smaller rating than the cable that they are protecting. This is BASIC stuff, yet probably one of the most important.
 
Admittedly I've only got the previous red OSG, but it sites 514.3 against 2.2.3 - Meter Tails. 514.3 is colour identification and has no comment regarding minimum cc's for tails, just like the rest of BS7671 as far as I'm aware.

What I am aware of is BS7671 giving us lots of guidance on how to design and calculate circuits properly as best befits the task in hand. But then, that takes more than a few days in a cram-class to understand.
 
I'm a bit lost here, if your feeding a small 2 way board for example and the loads are say 6 amp and 6 amp mcb. What's the point of using 25mm? If the loads never going to be over 12amps you can use a smaller csa tail to feed it
 
I'm a bit lost here, if your feeding a small 2 way board for example and the loads are say 6 amp and 6 amp mcb. What's the point of using 25mm? If the loads never going to be over 12amps you can use a smaller csa tail to feed it

because what if the small 2 way board was replaced with a larger load, eg a six way board, feeding a ring main, a couple of heaters etc. yes the responsible spark should check the tails feeding it but with the Electrical Trainee out there, would this actually happen. Like it quite clearly states in the regs all cables should be suitably protected.
 
because what if the small 2 way board was replaced with a larger load, eg a six way board, feeding a ring main, a couple of heaters etc. yes the responsible spark should check the tails feeding it but with the Electrical Trainee out there, would this actually happen. Like it quite clearly states in the regs all cables should be suitably protected.

Adam - we simply cannot future proof for every idiot out there in the world who is not as good at his job as we might be. If we did, imagine where we'd get to. AND - to what edition of reg's would we proof to - 18th? 19th? 20th?
 
I do agree somewhat but when you are talking 6mm tails fed from a 100 amp fuse, I think that's a bit extreme?
 

Reply to the thread, titled "small tails from service fuse" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top