I am finding this quite a complicated subject, and I would really welcome your thoughts on this subject.
If I could start with a TT system, according to regs, 411.5.3 states that when using an RCD for fault protection purposes, then the following has to be applied.
RaxIn<=50
This means that if we are using a 30ma rcd then Ra <= 50/0.03 = 1667 ohms earth loop impedance
Obviously they are concerned here with a poor earth connection, hence they have are using the safe voltage limit of 50v.
So for TT systems bs rcd to 4239 with a trip time of <= 0.2 are acceptable, 61008 with a trip time of 0.3 are not.
If i am using a circuit breaker for fault protection, say a 20amp 608686 then for TT i must use the following
ZsaxIa<= Uo 230/100 = 2.3 ohms.
I think what this means is basically if you have a good enough earth loop impedance then it is fine to use an mcb for 0.2 disconnection, instaneous operation being the all important word here, if not then use an rcd, and which is to my mind is treating the circuit then like supplementary bonding given the inclusion of the safe touch voltage.
For a TN system, where an earth is provided, then you must use
ZsaxIa<= Uo for both rcd’s and mcb’s, the regulations are quite clear about this, see 411.4.5
This leads to a pretty important finding for rcd’s the maximum loop impedance of which is 230/0.03 = 7667 ohms, now this is ridiculously high, and if I had an impedance of this, given that on TN systems the Ze should be 0.8 ohms, I would deffo investigate the r1+r2.
I can only conclude that 7667 ohms is a max hyperthetical figure, given there was issues around loop impedance with a Tn system that could be used to ensure instanteous disconnection with an rcd when used for fault protection.
What do you guys think of this 7667 ohms figure???
If I could start with a TT system, according to regs, 411.5.3 states that when using an RCD for fault protection purposes, then the following has to be applied.
RaxIn<=50
This means that if we are using a 30ma rcd then Ra <= 50/0.03 = 1667 ohms earth loop impedance
Obviously they are concerned here with a poor earth connection, hence they have are using the safe voltage limit of 50v.
So for TT systems bs rcd to 4239 with a trip time of <= 0.2 are acceptable, 61008 with a trip time of 0.3 are not.
If i am using a circuit breaker for fault protection, say a 20amp 608686 then for TT i must use the following
ZsaxIa<= Uo 230/100 = 2.3 ohms.
I think what this means is basically if you have a good enough earth loop impedance then it is fine to use an mcb for 0.2 disconnection, instaneous operation being the all important word here, if not then use an rcd, and which is to my mind is treating the circuit then like supplementary bonding given the inclusion of the safe touch voltage.
For a TN system, where an earth is provided, then you must use
ZsaxIa<= Uo for both rcd’s and mcb’s, the regulations are quite clear about this, see 411.4.5
This leads to a pretty important finding for rcd’s the maximum loop impedance of which is 230/0.03 = 7667 ohms, now this is ridiculously high, and if I had an impedance of this, given that on TN systems the Ze should be 0.8 ohms, I would deffo investigate the r1+r2.
I can only conclude that 7667 ohms is a max hyperthetical figure, given there was issues around loop impedance with a Tn system that could be used to ensure instanteous disconnection with an rcd when used for fault protection.
What do you guys think of this 7667 ohms figure???