Hi posted before
got loads of replies but still puzzzled on what we can do about feeding smoke alarms?
have put in some regs quotes from the excellent Amberleaf (please keep up the good work) and the confusing regs as usual.
"
Fire detection circuits must be supplied independently of other circuits and not protected by an Rcd protecting multiple circuits. 560.7.1
Fire detection cables, not including metal screened fire resistant cables, must be adequately segregated from cables supplying other circuits. 560.7.7
Except for TT systems, the circuit supplying a smoke alarm should not be protected by an RCD. For TT systems the smoke alarm must be supplied from the fixed equipment section of the ccu, not through a 30mA RCD. "
If we are to protect all circuits 30mA RCD if less than 50mm in depth of walls etc, how do we connect a smoke alarm in ccu bearing in mind the above, do we rcbo or mcb on a high integrity board any help on this confusion would be appreciated??
got loads of replies but still puzzzled on what we can do about feeding smoke alarms?
have put in some regs quotes from the excellent Amberleaf (please keep up the good work) and the confusing regs as usual.
"
Fire detection circuits must be supplied independently of other circuits and not protected by an Rcd protecting multiple circuits. 560.7.1
Fire detection cables, not including metal screened fire resistant cables, must be adequately segregated from cables supplying other circuits. 560.7.7
Except for TT systems, the circuit supplying a smoke alarm should not be protected by an RCD. For TT systems the smoke alarm must be supplied from the fixed equipment section of the ccu, not through a 30mA RCD. "
If we are to protect all circuits 30mA RCD if less than 50mm in depth of walls etc, how do we connect a smoke alarm in ccu bearing in mind the above, do we rcbo or mcb on a high integrity board any help on this confusion would be appreciated??