Had my ELECSA assessment yesterday and passed. The assessor mentioned it was preferable to put the smoke alarms on a lighting circuit. Thing is, in the building regs Document B 1.19 about power supplies(in brief) it says can be supplied either direct from the board or from a lighting circuit, but there should be a means of isolating power to the smoke alarms without isolating the lighting. What's the difference? The smoke alarms could still get left switched off :-o Although I agree you would notice if a fault made the lights go out. I'm thinking I should supply one light (such as the hall) from the RCBO for the smoke alarms and in addition to labelling up the board correctly, stick a note on the board warning that the hall light is seperate from the rest of downstairs lights.
I put it on a dedicated circuit as mentioned above the smoke's i use they bleep when no power is present and being run on batterys, just the way i do it.
What is the advantage of puttingit on a dedicated circuit?. I would have thought the advantage of being on a shared circuit outweighs dedicated supply
If it is on it own circuit the consumer has the ability to switch if off, which is dangerous, however if if it on a lighting circuit they cant just isolate it
Irish
I was at Elex in Exeter and Electrical Safety Council seminar recommended putting on lighting circuit and not on its own rcbo
It is a life saving bit of equipment so isolation is not an option I would suggest??
Irish
If the customer decides to switch off and doesnt know its a life saving equipment then they will be screwed when a fire breaks out.
Taken from the NICEIC tech manual
Clause 15.5(a) of BS 5839-6: 2004 recommends that the normal supply for a Grade D system should be derived from the public electricity supply, either via an independent circuit at the dwelling’s main distribution board with no other electrical equipment connected, other than a dedicated monitoring device to indicate failure of the normal supply, or a separately protected regularly used local lighting circuit. Clause 15.5(a) of BS 5839-6: 2004 recommends that the normal supply for a Grade D system should be derived from the public electricity supply, either via an independent circuit at the dwelling’s main distribution board with no other electrical equipment connected, other than a dedicated monitoring device to indicate failure of the normal supply, or a separately protected regularly used local lighting circuit.
So no to putting it on a lighting circuit;)
neil, your own post would sugest that you can use a regulary used local lighting circuirt.
either via an independent circuit at the dwelling’s main distribution board with no other electrical equipment connected, other than a dedicated monitoring device to indicate failure of the normal supply,or a separately protected regularly used local lighting circuit.
My smokes are on there own independent circuit and will beep when no power is available and the led on them changes to red.
Smoke Detectors - Own Circuit or Lighting?
Spudnik,
TEFFSAY,