snipped cpc`s | on ElectriciansForums

Discuss snipped cpc`s in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

diditrain

-
Arms
Joined
Jul 30, 2008
Messages
671
Reaction score
187
Location
north west
I have been asked to do a consumer unit change and have therefore done a bit of pre-work inspection and testing.
I have found a few minor issues which are easily rectified, however on one of the lighting circuits i have found that the cpc`s have been snipped right up to where the sheath has been stripped on the switch drops.
I am able to measure my zs at each lighting point but am unable to do it at the switch positons as the cpc is cut out.

Customer does not want the disruption of rewiring the switch drops so i feel that i will have to follow the protocol when the lighting circuits have no cpc present. Does this sound reasonable? Would appreciate others views on this issue.
 
As long as there was no metal switch plates should be ok may be worth just making a note on the cert to cover yourself incase when you finish they follow you round and replace the plasic switches with metal ones.
 
As you know regulation 412.2.3.2 does say that a CPC should be present at each point of an installation even if you use class II fittings.

But I think by changing the old CU, and assuming that CU does not have RCD protection, then by fitting RCD protection you are making the installation safer.

Now you will get get arguments that customer not wanting disruption of his house is not a way round the regs, and the other side of the argument will be you are leaving the installation safer.

For me I would be doing a risk assessment, can you perhaps get a 1mm G/Y single down to the switch via the tubing of the switch, have a try, if it is impossible then I would be still changing the CU, put a label at the CU saying about the CPC situation and finally on your EIC in the part about "comments on existing installation" and the "departures from BS 7671-2008" make an ote, with the relevant reg departure

Also this might be of use as a guide in the future

http://www.the50plus.co.uk/tech_support/best_practise_guides/BPG1_08.pdf
 
Im not sure the last paragraph which relates to CPC's being run to and terminated at each point in wiring and at each accessory relates directly to exposed-conductive-parts nor insulation classes. Is it not more of a general requirement under the heading of protective earthing?
 
I have to admit Gary that the last paragraph can be interpreted to not just include exposed conductive parts but I always felt that as the other parts of the protective earthing section mention these exposed conductive parts and that the last part also includes the term then that is what it is referring to.

I have no problem if someone also wanted to include this reason on an EIC for a circuit without a CPC, but as 412.2.3.2 deals with the circuit as a whole I would use that one
 
Correct me if wrong, but any part of the circuit you work on has to be brought up to code?

To me that means if you are swapping a db, you pretty much have to ensure that the whole installation is compliant.
 
Correct me if wrong, but any part of the circuit you work on has to be brought up to code?

To me that means if you are swapping a db, you pretty much have to ensure that the whole installation is compliant.

everything brought up to code no. Equipotential bonding yes.

Just imagine all the work if every house you touched had to be brought up to the 17th?? - its wouldn't do you, or the business any good what so ever.
 
Had this many times over the years and many were cut at the light end also so best to check, normally you can pull enough slack down the tube to get a crimp on and extend to the earth terminal. In 25yrs one's never beaten me yet. Or you could wimp out and put it on the cert. ;)
 

Reply to snipped cpc`s in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top