You make a good point and thats what i threw this question out there for, a thought i overlookedWhat about the cpc in a spur? do you run a seperate 4mm earth.

You make a good point and thats what i threw this question out there for, a thought i overlookedWhat about the cpc in a spur? do you run a seperate 4mm earth.
It would seem to me that in most cases here the answers that Darkwood recieved were not for the the question asked, Hocome on lads read the question properly before answering
Much appreciated, for the back-up as you say the answers went straight off on a tangent that why i had to re-enforce the question 3 times but end of day its all fun and in no way puts me off as i got there in the endIt would seem to me that in most cases here the answers that Darkwood recieved were not for the the question asked, Hocome on lads read the question properly before answering
That is correct as you say Darkwood. Cpc conductors from ring must be terminated at socket not back box. Then fly lead if required.
If i came accross sockets terminated like that whilst doing a PIR i would code 2 it and therefore PIR would be unsatisfactory.