can u use 1.5mm cable feeding a single socket from the DB on a 16a breaker?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss socket in 1.5 in the Australia area at ElectriciansForums.net
But will it "kick in" after 16 A vernam? I thought MCBs to BS EN 60898 will take overcurrent to 1.45 times the rated for upto an hour before going.....Such a simple question has turned into a 4 page debate
Im confused as to why people are asking what load is going to be on it and designating it by label etc....
Without doing the calcs the maximum load permissable through a 1.5mm is 19A, so wire it in 1.5mm, regardless of what you plug in to it, DVR or no DVR, kettle or toaster, by fitting a 16a mcb, overload protection will kick in after 16a to protect the cable, i dont see why people have "foggied" the question ?
why not just put it on a 6A MCB?
Anyone lost the will to live yet??