Such a simple question has turned into a 4 page debate

Im confused as to why people are asking what load is going to be on it and designating it by label etc....

Without doing the calcs the maximum load permissable through a 1.5mm is 19A, so wire it in 1.5mm, regardless of what you plug in to it, DVR or no DVR, kettle or toaster, by fitting a 16a mcb, overload protection will kick in after 16a to protect the cable, i dont see why people have "foggied" the question ?
But will it "kick in" after 16 A vernam? I thought MCBs to BS EN 60898 will take overcurrent to 1.45 times the rated for upto an hour before going.....
 
This is proving to be a good debate however the original question although very open

"can u use 1.5mm cable feeding a single socket from the DB on a 16a breaker?"

I would say has been answer by many - yes

That said we all, (I believe) would use 2.5 for the wiring of any sockets
 

Reply to socket in 1.5 in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
318
My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
986

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top