I have a socket in a house showing up as live on both ring 1 and ring 2 ? powered up the house today and used a socket tester and it was flashing on both rings when I isolated each one on their individual MCB’s ? does anyone know what this could be ?
 
I have a socket in a house showing up as live on both ring 1 and ring 2 ? powered up the house today and used a socket tester and it was flashing on both rings when I isolated each one on their individual MCB’s ? does anyone know what this could be ?
Possibly a result of connecting it across two circuit breakers having failed to carry out initial verification before putting the installation into service. That would seem like the most likely explanation, although socket testers aren't necessarily hugely accurate but rather indicative.
 
Possibly a result of connecting it across two circuit breakers having failed to carry out initial verification before putting the installation into service. That would seem like the most likely explanation, although socket testers aren't necessarily hugely accurate but rather indicative.
The continuity was ok on ring 1 but not showing on the lives on ring 2 ? it’s very confusing . So I think the connection was ok
 
There is also the possibility of damage to cables,which could cause this - either way,it needs detailed investigation,in a methodical manner.
 
Recently had a job where there is 3 rfc in the house and all 3 were interconnected. So in short no matter which 32a fuse you pulled all the sockets remained live.
I have temporarily put the entire lot onto one circuit to make isolation easier.
Going to be a right pig to sort out
 
each end of the ring is connectted to a different breaker,
if both of those breakers come from the same source ?
that would explain why he has gotten away with it !
But it is potentually dangerous and needs to be correctted.
This requires methodical thinking and testing
So best left to a good electrician.
 
Last edited by a moderator:
I have a socket in a house showing up as live on both ring 1 and ring 2 ? powered up the house today and used a socket tester and it was flashing on both rings when I isolated each one on their individual MCB’s ? does anyone know what this could be ?
It looks like the two ring circuits are crossed with one another,and the person who installed the rings did not verify ring continuity.
 

Reply to Socket showing live on both ring mcb’s ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
439
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yes that will do the job - presuming there is a battery in it and it's working Ok! Turn the rotary knob one click to the V setting as you say...
2
Replies
22
Views
2K
  • Question
Recommend this: Electricians Guide to Inspection and Testing Book -...
2
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top