M
Moses
I'm not disagreeing with the need to try and find out why the Zs is high but:
411.4.4 - An RCD can be used for fault protection with an overcurrent protective device also in place.
When does anybody measure the Z between neutral and line to ensure that an MCB will trip? The only measurement you make is Isc at the origin!
Zs is always measured between CPC and L conductors.
This is because, in UK we use a reduced size CPC, so if the Zs is ok when measured with CPC-L fo a fault current, then its obviously OK between L-N for a short circuit current!!!