Sorry tried to edit my last post but it did not appear.

The socket is part of the ring circuit. The cabling is exactly the same on all sockets. It is a TNC-s system, I pushed the plug of the tester in and out numerious times so hopefully no tarnished connections. I also took reading from rear of socket. The DB is a MCG fuseboard with a 2P6330 RCD and 2 x 60898 mcb’s 1x 20Amp 1 x 6Amp. What is the table or reg that says about rcd controlled socket can be 1667 ohms.
 
Am I missing something?

Shouldn't the reading be 0.35 (or even less with parallel paths) at all the sockets?


1666 ensures the RCD will disconnect before voltage rises above 50V.
It should not be used to ignore maximum Zs values - unless unavoidable (e.g. TT)
 
pushed the plug of the tester in and out numerious times so hopefully no tarnished connections

I meant where the cables terminate in the back of the SO too, as your end to end readings were ok.

What is the table or reg that says about rcd controlled socket can be 1667 ohms.

Table 41.5 (BGB) p57.

It actually says anything above 200 may be unstable wrt Earth rods.

Edit: Tel beat me to it, again! lol
 
Last edited:
the 1667Ω figure is for earth faults, and not for live-n faults. I would carry out a Zp-n, which means that you test between live and neutral, not live and earth. If your using a fluke, its just a case of swapping the leads over, but if its a megger, then youll have to use the probes. If this comes up ok, then youve identified that it is indeed a problem with the earth path, and not the live. If it comes up bad, then it means that you have problems wiuth either your live or neutral.
 
As its a socket should be on a RCD anyway, in which case Zs up to 1667ohms.

Not Correct!

RCD is backup / supplementary protection to the main protection.

Will the RCd trip the circuit? when there is a shortcircuit? and the cable burns the house down?
because the CB did not trip, because the Zs was too high?:laugh3:
 
Last edited by a moderator:
This log cabin, does it have it's own metered supply? Or, is it fed by a distribution circuit from another building?

If the latter, then what is this Ze you quote? Ze at the supply or at the cabin board (ie Zdb)?

Looks to me like we're missing some info.

Anyway up, those Zs figures (assuming that's what they are, you don't state explicitly) are somewhat astray. Poor or varying Zs at sockets can be due to bad connections at the pins or dirt/corrosion on the switch contacts. Have you tried flicking the switches a few times to 'clear' the contacts?
 
Not Correct!

RCD is backup / supplementary protection to the main protection.

Will the RCd trip the circuit? when there is a shortcircuit? and the cable burns the house down?
because the CB did not trip, because the Zs was too high?:laugh3:

I'm not disagreeing with the need to try and find out why the Zs is high but:

411.4.4 - An RCD can be used for fault protection with an overcurrent protective device also in place.

When does anybody measure the Z between neutral and line to ensure that an MCB will trip? The only measurement you make is Isc at the origin!
 
Not Correct!

RCD is backup / supplementary protection to the main protection.

Will the RCd trip the circuit? when there is a shortcircuit? and the cable burns the house down?
because the CB did not trip, because the Zs was too high?:laugh3:
your not measuring line voltage or short circuit with a Zs Moses.....
 

Reply to Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top