Hi Rich,
The OP never said if he did the (R1+R2) dead tests at each socket, I did ask.
The overall end to end and crossover readings r1 and r2 and R1+R2 were about correct and not too far out when added to the Ze.
My next move would have been to temporarily put the pairs of the Hi Z S/O conductors into three seperate Chock blocks or similar to see if I got more sensible/expected readings, and then replace the S/O if necessary.
I have had it before where the conductors have been twisted together giving reasonable end to end results, but poor at the S/O (slack terminal screw), or the odd time where the S/O terminal has suffered due to dampness/corrosion and gave poor or high readings, yet the end to end readings have been again reasonable.
The OP never said if he did the (R1+R2) dead tests at each socket, I did ask.
The overall end to end and crossover readings r1 and r2 and R1+R2 were about correct and not too far out when added to the Ze.
My next move would have been to temporarily put the pairs of the Hi Z S/O conductors into three seperate Chock blocks or similar to see if I got more sensible/expected readings, and then replace the S/O if necessary.
I have had it before where the conductors have been twisted together giving reasonable end to end results, but poor at the S/O (slack terminal screw), or the odd time where the S/O terminal has suffered due to dampness/corrosion and gave poor or high readings, yet the end to end readings have been again reasonable.