"I think you must agree, that if 6A a breaker will trip with a 7A fault current(CPC-L), then it surely will trip with a 8A current short circuit(L-N)."
Will it?????
ever???
in 0.4s ??
Will it?????
ever???
in 0.4s ??
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Am I missing something?
Shouldn't the reading be 0.35 (or even less with parallel paths) at all the sockets?
1666 ensures the RCD will disconnect before voltage rises above 50V.
It should not be used to ignore maximum Zs values - unless unavoidable (e.g. TT)
Totally agree, should be getting a Zs of around 0.35ohms at each socket outlet. Sounds like a loose connection at one of the sockets.....
high Z...well that`s changed then....a minure ago it was Zs....Thank god we r on the same page
I agree with your comment of a Hi z on the N wire.
But that's another reason why Zs is measured between L-CPC, it ensures the earth fault durations are limited.
Not true!!!
R1+R2 should be the same at each socket outlet. Zs will increase towards the middle of the ring and decrease back towards the DB therefore you will get a reading of around 0.35Ω near the middle of the ring.
"I think you must agree, that if 6A a breaker will trip with a 7A fault current(CPC-L), then it surely will trip with a 8A current short circuit(L-N)."
Will it?????
ever???
in 0.4s ??
Agreed to a point (Hence "around" 0.35ohms)
I believe the ring in question is fairly small and the figures the op states seem way off by 1 and a bit ohms....seems alot to me, especially as he states these sockets are all on the ring final and not spurs.
Points to something along those lines agreed....where is the OP????
so if he hasn`t `zeeored`...or the batterys are low....hmm, so its a faulty meter then is it Moses?....possibly...but rather than just condemn the meter..would you not check the leads first?....Sipmles he has not zeeored
or
he has a low battery
or
He has a faulty meter
but my point was you dont just condemn the meter....its only as good as the test leads you are using....
Yes, I'm sorry. I should have written -Geoff, my friend, Zs is the impedance of the circuit, and not a current.
Reply to Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net