oh, table 52.3 which states minimum sheathed cable for power circuit is 1.0mm?do you mean that one?as for the 433.1.1 I can't see anything relevant other than the protective device should be appropriate for the cable size-
Look again mate.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss sockets wired in 1.0mm 3 core flex in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
oh, table 52.3 which states minimum sheathed cable for power circuit is 1.0mm?do you mean that one?as for the 433.1.1 I can't see anything relevant other than the protective device should be appropriate for the cable size-
why would a load need to be midway in a ring to avoid overloading??that's the point of a ring, that every point is the same in regards to any load upon it.I find that worrying that someone would think otherwise
Have you EVER given a useful piece of advice to anyone? or do you get your jollies by trying to appear superior to everyone else? do us all a favour and get a life. I've been an electrician most my life and know what a ring should be wired in. I was simply wondering about any options in regards to the flex.noone has yet proved that it's against the regs but I know it'll have to go
Des 56 - I may have misread something ...
There are four options:
1) Rip out and replace.
2) De-rate the CPD.
3) Disconnect and leave alone.
4) Leave as is and do nothing.
You've already stated that ripping out and replacing is not an option.
It's been pointed out to you what the maximum rating of CPD should be if you de-rated, but you appear to be having trouble understanding the reasons.
That leaves you with disconnection or leaving as is.
Just to set your mind at rest, as has already been pointed out by others, there is nothing in the Regulations prohibiting the use of flex for fixed wiring.
The only reason (from the information you have provided) that the situation doesn't comply is that the CPD is rated too high for the conductors used.
Reply to sockets wired in 1.0mm 3 core flex in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net