S
solarfred
Here is a fully compliant system running 9 (yes 9) immersion heaters only using PV power. 3 phase system with house on one phase (so EMMA was not going to work). The power is from 27kw array and heating 3000 litre store for swimming pool and then surplus into house DHW. Not one for the purists but it was a project I had to accept.
The pool house is 70 metres from the inverters and the CT clamps measuring all three phases for PV and house loads. The system runs via RF to the sockets.
We have it running but are now fine tuning. I have got them to install 3 x 1.5kw elements in the first switches so as to get it working virtually all the time with the rest 3kw elements.
We can set the time of operation per day/ the time delay of switching from 0 minutes upwards (to allow for brief interruptions) / balance of power switching point in watts. Stepped switching so as power changes the immersions switch on or off to keep it all positive.
Key is getting the programme correct so as to minimise the export potential. As customer is getting paid for production and deemed export so a little bit of export is allowable! Import is a no, no.
The pool house is 70 metres from the inverters and the CT clamps measuring all three phases for PV and house loads. The system runs via RF to the sockets.
We have it running but are now fine tuning. I have got them to install 3 x 1.5kw elements in the first switches so as to get it working virtually all the time with the rest 3kw elements.
We can set the time of operation per day/ the time delay of switching from 0 minutes upwards (to allow for brief interruptions) / balance of power switching point in watts. Stepped switching so as power changes the immersions switch on or off to keep it all positive.
Key is getting the programme correct so as to minimise the export potential. As customer is getting paid for production and deemed export so a little bit of export is allowable! Import is a no, no.