John-SJW

Surge protection is now semi-mandatory in domestic (there are get out clauses).
Is SPD mandatory, or semi-mandatory, in commercial offices?
 
I can tell you that the same process should be carried out as for domestic premises, but that’s simply from following the regulations and we’ve already established you’re not keen on that.

To clarify, that’s 443.4 where single dwellings are excepted from the requirements to perform a risk assessment. You need to carry out a risk assessment or if you decide not to carry out a risk assessment you need to provide transient overvoltage protection.
 
Last edited:
I recently had a similar question. Part of my journey towards the answer in my particular case was this short article:
 
I agree with @Doomed
In many cases if you cost the time to perform the risk assessment and go through the options with your client (including getting the value of equipment they have that is susceptible to damage, and the cost implications of lost business due to damage-induced down-time, etc) it will cost about the same as fitting a type 2 SPD anyway!

Edited to add: If they have a lightning protection system to need type 1 SPD then it has to be fitted anyway. Though some remote sites with lots of lightning activity might be better served with a type 1 so it lasts longer.
 
What happens if their electronic equipment still goes bang in a lighting storm
Their problem, as you have done your bit.

Most electronics should survive at least the CAT-II sort of surges, but some are simply crap, and others are also vulnerable to damage though data lines (cable TV coax, phone line, etc) so would need separate protection.

You can harden electronic installations to survive a direct hit and keep going, but not domestic installations for sure!
 
Have other services as phone, cable tv adopted this too?
Don't know about cable TV, but traditional phone lines always had SPD at the master socket and there are standards for the sort of spikes that telecoms stuff should handle.

Though I suspect that has gone from newer systems. Probably BT, etc, treat the modems as disposable - they often don't update the crap software anyway!
 
From the archive of "here is one prepared earlier" we installed a system in Italy in 1995 and upgraded its computers and radio part in 2005. In 2019 I went out to repair it as they said it stopped working in one of its frequency bands, but the antenna was still tracking and working in the other.

Only later did they admit that it happened at the same time as a lightning storm.

Then when I got there and took down the front-end (bit that sits at the focus of a dish-style antenna) to replace the failed low-noise amplifier I found this melted spot where it actually had been hit:
IMG_20190129_173140773.jpg


Here is a photo of what that metal cover has inside:
IMG_4623.JPG
 
We had put some effort in to protecting it against induced lightning surges, but never thought it would have survived a direct hit!

This was not really planned for, and the bureaucracy of trying to get the institute to fit some protection (and find the budget to do so) was a problem. The building itself was protected, but the antenna was now the highest point.

So we made up a makeshift LPS using stuff from local hardware shops, in between ice-creams and coffees, and hopefully it will be OK for the future:
makeshift-lightning-protection.jpg
 
What happens if their electronic equipment still goes bang in a lighting storm
In a commercial set up the installation should be set up in zones, each one designed to step down the surge current to a tolerable level at the equipment.

MDMImage.png


Same can be applied in domestic by using type 3 surge protected outlets.
 
We had put some effort in to protecting it against induced lightning surges, but never thought it would have survived a direct hit!

This was not really planned for, and the bureaucracy of trying to get the institute to fit some protection (and find the budget to do so) was a problem. The building itself was protected, but the antenna was now the highest point.

So we made up a makeshift LPS using stuff from local hardware shops, in between ice-creams and coffees, and hopefully it will be OK for the future:
View attachment 86202
Nice idea, I'm surprised they wouldn't just stump up for a couple of finials, they tend to be a lot cheaper than the damaged caused by a strike.
 
Nice idea, I'm surprised they wouldn't just stump up for a couple of finials, they tend to be a lot cheaper than the damaged caused by a strike.
Ideally they would have had it done when the building LPS was updated at some point between our original installation and when we had to fix it. We saw the change in conductors, etc, but no thought about a point going above the antenna! There you go :(

Our make-shift one is not ideal, as it would provide weak protection from some directions as not high enough and no time / spare cash to put in a couple of them. But it was the first direct hit in over 20 years so not that common.
 
others are also vulnerable to damage though data lines (cable TV coax, phone line, etc) so would need separate protection.

That has always been my concern. OK SDP may save boiler pcb's and LED lights, but the expensive stuff is still vulnerable via data cables.
 
Last edited by a moderator:
That has always been my concern. OK SDP may save boiler pcb's and LED lights, but the expensive stuff is still vulnerable via data cables.
It is less common now, as networking is mostly wireless or Ethernet (which is usually isolated and can take kV level spikes) within a building, and usually these days fibre between network switches in different buildings (or sometimes between floors of a building) which is to all intents and purposes immune to surges.

PoE Ethernet is more vulnerable due to the DC path for the power. Also commonly seen is RS232 / RS422 used for industrial plant, but they are often OK if not running hundred or more meters, or (more seriously) between buildings. Well-bonded cable try also helps to divert some of any induced surges away from the signal cables.

Again, not really domestic!

For domestic the risks for surges, outside of the AC power lines, are TV/satellite antennas/CCTV (really only if hit) and cable TV / telephone lines (as they run for long distances outside of the building).
 
So what the guidance is saying Johnboy, do a risk assessment of clients electronic equipment (cost)and ask them isit worth it or not.

They should sign it too.
Having seen a hospital take a substantial lightning strike with a repair bill of circa £500,000 and about 4 - 5 days disruption there was a full risk assessment done on the future risk of it happening again the results of which concluded that the cost (around £600,000) of installing the necessary protection across the site versus the strike risk was not a viable spend having had no documented strikes in the previous 40 - 50 years and a calculated future strike risk of 1 sometime in the next 44 to 400 years
Got caught out on my NIC assessment in 2019 for not fitting them on a commercial job.

No, just stearnly told us to do risk assessments in future on an individual basis (ie, for the cost and hassle of doing the assessment and getting approval from the client NOT to fit it its just easier to go ahead and fit surge and charge a bit more for the job)
Sounds like the NIC trying to make a point and help the manufacturers sell more, I'm surprised the NIC are not insisting on professional indemnity for contractors in case they fit the wrong type of SPD

What happens if their electronic equipment still goes bang in a lighting storm
Anyone for efficacy insurance if the SPD fails to operate under surge / strike conditions
Don't know about cable TV, but traditional phone lines always had SPD at the master socket and there are standards for the sort of spikes that telecoms stuff should handle.

Though I suspect that has gone from newer systems. Probably BT, etc, treat the modems as disposable - they often don't update the crap software anyway!
I've seen a lot of surge arrestors fitted on intruder alarm comms kit where the installer didn't bother to connect them to a suitable earth so it made them a bit useless
Ideally they would have had it done when the building LPS was updated at some point between our original installation and when we had to fix it. We saw the change in conductors, etc, but no thought about a point going above the antenna! There you go :(

Our make-shift one is not ideal, as it would provide weak protection from some directions as not high enough and no time / spare cash to put in a couple of them. But it was the first direct hit in over 20 years so not that common.
I've worked on a number of sites with rooftop comms kit and while installing comms kit I got into the habit of doing a quick test on the LPS down lead after we had some interference problems on one site where all the comms cables going to a number of buildings were earthing the LPS at the indoor units because the LPS down lead connection to the earth rod was broken and this was on an LPS that had been tested and certified some 10 months earlier the customer was adamant that it was ok and waved the certificate at me so I got a spade out and exposed the corroded LPS earth connections and then had to more or less drag him out of his office across the site to show him the problem that we had found
I just looked at John Ward's Youtube vids on SPDs - has series of about five vids on SPDs, emphasising how essential it is. He goes into the zones aspect. Worth looking at.
Based on what risk assessment and likely hood of it actually happening

When you look at the cost of an SPD I suppose it could be classed as an insurance policy that could sit there for many years and may never ever be needed so how do you justify the cost to the customer. As installations are altered and modified should the risk assessment be revisited to confirm that the type of SPD's installed are suitable for what may be a changed risk within the installation or whether the changes mean an SPD should be installed, which is something that no doubt will be addressed in future guidance

The combined industry experience of this forum probably runs to many hundreds if not thousands of years so the question is how many jobs have members been to where SPD's may have or would have prevented equipment damage and then would the cost of installing SPD's v's the replacement / repair cost of the equipment and disruption caused made it a cost effective decision to install SPD's
Personally in all the years I have worked in the industry I have only seen less than a handful of incidents that may have benefited from an SPD being installed so why is the push now to suggest that sites are at a much greater risk
 
I thought if you covered the incommer the rest is just optional.
An SPD will not fully stop a surge, it steps it down to a more manageable level.

I've lifted this from the Hager SPD guide:

• Type 1 - SPD which can discharge partial lightning current with a typical waveform 10/350 μs. Usually employs spark gap technology.

• Type 2 - SPD which can prevent the spread of overvoltages in the electrical installations and protects equipment connected to it. It usually employs metal oxide varistor (MOV) technology and is characterized by an 8/20 μs current wave.

• Type 3 – These SPDs have a low discharge capacity. They must therefore only be installed as a supplement to Type 2 SPD and in the vicinity of sensitive loads. Type 3 SPD’s are characterised by a combination of voltage waves (1.2/50 μs) and current waves (8/20 μs).

In a nutshell, Type 1/2 at the incomer to protect the installation and Type 3 to protect the current using equipment.
 
The combined industry experience of this forum probably runs to many hundreds if not thousands of years so the question is how many jobs have members been to where SPD's may have or would have prevented equipment damage and then would the cost of installing SPD's v's the replacement / repair cost of the equipment and disruption caused made it a cost effective decision to install SPD's
Had one customer, of a previous employer, who would call us out at least once a year to replace a faulty rectifier module on one of their sites just north of Carlisle. After the third incident I decided to do a little research and the site alarm would trigger a rectifier fail everytime there was an electrical storm in the area.

We recommended fitting SPDs, the site has it's own LP system but it was installed long before SPDs were required. The customer declined due to cost, but each rectifier module was just over £2k to replace, but on a different budget...

This was a dark fibre switching site for a major fibre network supplier so a critical location, they risk potentially millions in lost revenue per hour if the site goes down but penny pinch on infrastructure...
 
When you look at the cost of an SPD I suppose it could be classed as an insurance policy that could sit there for many years and may never ever be needed so how do you justify the cost to the customer.
To some extent this is how I see it. These days many domestic CU have them already fitted, or they are around £50 more, so on a board change it is typically under 10% of the cost and could well save that in years to come.

However, I have always been a bit paranoid about circuit protection as over the years we put in stuff in locations that suffer far more than the UK in this respect. For example, we had stuff in Malaysia where you got major lightning storms practically every 2nd afternoon! Even as I first saw the country on leaving the airport I noticed how big and deep the road side gutters were, and within a couple hours saw why!

For that system we had to retrofit more protection, and so from then on we assumed the worst and designed it in.

Personally in all the years I have worked in the industry I have only seen less than a handful of incidents that may have benefited from an SPD being installed so why is the push now to suggest that sites are at a much greater risk
I think the change is now we are seeing far more easily damaged stuff being used in homes. LED lighting, an array of expensive electronics goods, and most white-goods are now controlled by complex solid-state systems. Also they are getting cheaper and nastier by design as they get "value engineered" to save a couple of pence here and there.

Yes, at least we have the EMC directive singe 1996 that finally mandated some degree of immunity as a requirement, but a lot of cheaper stuff I would be fails to meet it and no one does anything :(
 
I've seen a lot of surge arrestors fitted on intruder alarm comms kit where the installer didn't bother to connect them to a suitable earth so it made them a bit useless

I've worked on a number of sites with rooftop comms kit and while installing comms kit I got into the habit of doing a quick test on the LPS down lead
Indeed! This should be the FIRST point when looking to install!

Without a good low impedance (dominated by inductance) earth the SPD are often ineffective, to the point of potentially being useless (or even dangerous, if internal metalwork becomes many kV on a surge).
 
Last edited:
The insurance companies are going to have to suck it up and obviously charge. You cant tell people you need this to save your electronic equipment and it doesn't work.

I'd say are own personal indemnity insurance will be attacked. They be Waiting for lighting in area and false claims to arise..
 
Having seen a hospital take a substantial lightning strike with a repair bill of circa £500,000 and about 4 - 5 days disruption there was a full risk assessment done on the future risk of it happening again the results of which concluded that the cost (around £600,000) of installing the necessary protection across the site versus the strike risk was not a viable spend having had no documented strikes in the previous 40 - 50 years and a calculated future strike risk of 1 sometime in the next 44 to 400 years



Sounds like the NIC trying to make a point and help the manufacturers sell more, I'm surprised the NIC are not insisting on professional indemnity for contractors in case they fit the wrong type of SPD


Anyone for efficacy insurance if the SPD fails to operate under surge / strike conditions

I've seen a lot of surge arrestors fitted on intruder alarm comms kit where the installer didn't bother to connect them to a suitable earth so it made them a bit useless

I've worked on a number of sites with rooftop comms kit and while installing comms kit I got into the habit of doing a quick test on the LPS down lead after we had some interference problems on one site where all the comms cables going to a number of buildings were earthing the LPS at the indoor units because the LPS down lead connection to the earth rod was broken and this was on an LPS that had been tested and certified some 10 months earlier the customer was adamant that it was ok and waved the certificate at me so I got a spade out and exposed the corroded LPS earth connections and then had to more or less drag him out of his office across the site to show him the problem that we had found

Based on what risk assessment and likely hood of it actually happening

When you look at the cost of an SPD I suppose it could be classed as an insurance policy that could sit there for many years and may never ever be needed so how do you justify the cost to the customer. As installations are altered and modified should the risk assessment be revisited to confirm that the type of SPD's installed are suitable for what may be a changed risk within the installation or whether the changes mean an SPD should be installed, which is something that no doubt will be addressed in future guidance

The combined industry experience of this forum probably runs to many hundreds if not thousands of years so the question is how many jobs have members been to where SPD's may have or would have prevented equipment damage and then would the cost of installing SPD's v's the replacement / repair cost of the equipment and disruption caused made it a cost effective decision to install SPD's
Personally in all the years I have worked in the industry I have only seen less than a handful of incidents that may have benefited from an SPD being installed so why is the push now to suggest that sites are at a much greater risk
At 12 mins John Ward explains why these day SPD is important. Dave Savery on one of his vids fitted SDP under an assumption spikes were causing expensive LED lamps to fail too frequently. It was fitted then no problems. How many expensive pcb boards in boilers would have been saved if SDP was fitted? Not to ention being cold and no hot water. mmmm Expensive components may have failed, yet we do we attribute the failure to a spike!

 
Last edited by a moderator:
Having seen a hospital take a substantial lightning strike with a repair bill of circa £500,000 and about 4 - 5 days disruption there was a full risk assessment done on the future risk of it happening again the results of which concluded that the cost (around £600,000) of installing the necessary protection across the site versus the strike risk was not a viable spend having had no documented strikes in the previous 40 - 50 years and a calculated future strike risk of 1 sometime in the next 44 to 400 years

Lightening can strike the earth then affect underground cables quite frequently giving spikes. There does not need to be a full building strike or a direct strike onto a cable. These frequent strikes can be arrested by the SPDs.
 
Having seen a hospital take a substantial lightning strike with a repair bill of circa £500,000 and about 4 - 5 days disruption there was a full risk assessment done on the future risk of it happening again the results of which concluded that the cost (around £600,000) of installing the necessary protection across the site versus the strike risk was not a viable spend having had no documented strikes in the previous 40 - 50 years and a calculated future strike risk of 1 sometime in the next 44 to 400 years
Between 1942 and 1977, Sullivan was hit by lightning on seven occasions and survived all of them.
 
At 12 mins John Ward explains why these day SPD is important. Dave Savery on one of his vids fitted SDP under an assumption spikes were causing expensive LED lamps to fail too frequently. It was fitted then no problems.
A really scientific approach to solve a problem then, so lamps failed then they didn't after the SPD was fitted so could it have been..............................a bad batch of lamps!
It is one of those situations were a power quality analyser with a before and after analysis may have given it a bit more credibility
How many expensive pcb boards in boilers would have been saved if SDP was fitted? Not to ention being cold and no hot water. mmmm Expensive components may have failed, yet we do we attribute the failure to a spike!
Most of the failed boiler PCB's I've seen are down to crap soldering during manufacture causing high resistance joints that overheat and burn the board
Between 1942 and 1977, Sullivan was hit by lightning on seven occasions and survived all of them.
Did he have an SPD fitted??
 
A really scientific approach to solve a problem then, so lamps failed then they didn't after the SPD was fitted so could it have been..............................a bad batch of lamps!
That approach worked. I am not sure if he said he contacted the local weather people to see if there were many lightning strikes about.

Interesting comment on John Ward's vid......

Thanks John, this is a great video, really helpful to explain the use of and requirement for surge protection. Very few people really realise the true extent & cost of damage caused by over voltage issues, one reason for that is that the UK insurance industry is very tight lipped about these things. In Germany this is not the case the insurance industry makes information freely available and they suggest that from all claims of "electrical or electronic damage" over voltage / surge issues are responsible for 31% of the claims. That is a huge figure, for anyone reading this and thinking "he's an idiot, I've never seen anything like that level of damage" ....well how do you know? Over voltage damage is not always immediate and spectacular, there may not be a huge bang and plumes of black smoke.

You can have several incidents over a few weeks and it would lead to wear and tear, then one day flick a switch on and the equipment doesn't work. Do you immediately think "oh that must be wear and tear fro over voltage events" of course you don't. You think "oh that's broken, more money to replace it /repair it". SPD's offer longer life spans for equipment, increased levels of availability, reduction in down time and less maintenance. They are like "electrical life assurance for equipment".
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
SPD in commercial offices
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36
Unsolved
--

Advert

Thread statistics

Created
John-SJW,
Last reply from
John-SJW,
Replies
36
Views
4,840

Advert

Back
Top