Surge protection is now semi-mandatory in domestic (there are get out clauses).
Is SPD mandatory, or semi-mandatory, in commercial offices?
 
I can tell you that the same process should be carried out as for domestic premises, but that’s simply from following the regulations and we’ve already established you’re not keen on that.

To clarify, that’s 443.4 where single dwellings are excepted from the requirements to perform a risk assessment. You need to carry out a risk assessment or if you decide not to carry out a risk assessment you need to provide transient overvoltage protection.
 
Last edited:
I recently had a similar question. Part of my journey towards the answer in my particular case was this short article:
 
I agree with @Doomed
In many cases if you cost the time to perform the risk assessment and go through the options with your client (including getting the value of equipment they have that is susceptible to damage, and the cost implications of lost business due to damage-induced down-time, etc) it will cost about the same as fitting a type 2 SPD anyway!

Edited to add: If they have a lightning protection system to need type 1 SPD then it has to be fitted anyway. Though some remote sites with lots of lightning activity might be better served with a type 1 so it lasts longer.
 
What happens if their electronic equipment still goes bang in a lighting storm
Their problem, as you have done your bit.

Most electronics should survive at least the CAT-II sort of surges, but some are simply crap, and others are also vulnerable to damage though data lines (cable TV coax, phone line, etc) so would need separate protection.

You can harden electronic installations to survive a direct hit and keep going, but not domestic installations for sure!
 
Have other services as phone, cable tv adopted this too?
Don't know about cable TV, but traditional phone lines always had SPD at the master socket and there are standards for the sort of spikes that telecoms stuff should handle.

Though I suspect that has gone from newer systems. Probably BT, etc, treat the modems as disposable - they often don't update the crap software anyway!
 
From the archive of "here is one prepared earlier" we installed a system in Italy in 1995 and upgraded its computers and radio part in 2005. In 2019 I went out to repair it as they said it stopped working in one of its frequency bands, but the antenna was still tracking and working in the other.

Only later did they admit that it happened at the same time as a lightning storm.

Then when I got there and took down the front-end (bit that sits at the focus of a dish-style antenna) to replace the failed low-noise amplifier I found this melted spot where it actually had been hit:
[ElectriciansForums.net] SPD in commercial offices


Here is a photo of what that metal cover has inside:
[ElectriciansForums.net] SPD in commercial offices
 

Reply to SPD in commercial offices in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It looked like the live connection side ( internally) burned against the neutral of the main switch
2
Replies
23
Views
1K
  • Question
You'd have to be mindful of SPD conductor lengths doing it that way. I think Matt:E make a single board with Type A RCBO, openPEN detection and...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top