Ok need advice.

Two domestic consumer units both fed of same Escos ideally should only have been one but she to it being an older house and the location of DNO equipment this was not possible without unreasonable expense. As both are beside each other and fed from same Escos could 1 SPD 2 in one consumer unit service the circuits on both boards???

Any help be appreciated.

J
 
Ok need advice.

Two domestic consumer units both fed of same Escos ideally should only have been one but she to it being an older house and the location of DNO equipment this was not possible without unreasonable expense. As both are beside each other and fed from same Escos could 1 SPD 2 in one consumer unit service the circuits on both boards???

Any help be appreciated.

J
One spd should benefit both.
 
What is the total length of cable between Lin at the isolator of the non-SPD board, via the SPD in the other board, to earth?
It's supposed to be less than 50cm.
I suspect your suggestion might result in less protection for the second board.
The boards are literally beside each other. Maybe a difference of 10/15 cm tails from same Henley Blocks. DNO is NIE (Northern Ireland) wanted to charge 300 quid to move the meter and head.
 
The boards are literally beside each other. Maybe a difference of 10/15 cm tails from same Henley Blocks.
Just to emphasise the 50cm 'rule' I was talking about, some theory below. A surge is shunted to earth, so the length of the earth connection used is part of the calculation. So distance of Lin of second CU to Lin of first CU (if that's where the SPD is going), plus distance from Lin to MCB protecting SPD, plus distance MCB out to SPD, plus distance from SPD earth terminal to main earth bond. All those added together is supposed to be less than 50cm, and if it is that, the household could still get a 500V surge on top of the mains voltage (strictly on top of the SPD cut-in voltage)!


IMG_0745.jpeg
 
Just to emphasise the 50cm 'rule' I was talking about, some theory below. A surge is shunted to earth, so the length of the earth connection used is part of the calculation. So distance of Lin of second CU to Lin of first CU (if that's where the SPD is going), plus distance from Lin to MCB protecting SPD, plus distance MCB out to SPD, plus distance from SPD earth terminal to main earth bond. All those added together is supposed to be less than 50cm, and if it is that, the household could still get a 500V surge on top of the mains voltage (strictly on top of the SPD cut-in voltage)!


View attachment 118111
Regulation 534.4.8 SPD installation shall
preferably not exceed 0.5m and in no
case exceed 1m
 

Reply to the thread, titled "SPD2" which is posted in Domestic Electrician Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
SPD2
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
6
Unsolved
--

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Jonny72,
Last reply from
mainline,
Replies
6
Views
693

Advert

Back
Top